    Climaventa focs/sl-bt/s 1702
    We have the above chiller at our plant. It is showing an error. The error is '401 PROBE ERROR'. The unit still seems to be working correctly but has this error on the display. I can not find the manuals that came with the install. Can anyone please help.
    Somerset
    63
    4,518
    38
    Re: Climaventa focs/sl-bt/s 1702
    Hi Mark
    400 alarms are a temperature probe error Fault
    That's if it has the 3000 series controller fitted.
    I will send you some info.
    Jan 2014
    United Kingdom
    47
    26
    Thanks Grizzly
    will let you know how we get on
    Jan 2014
    United Kingdom
    47
    26
    it is fitted with W3000 compact controller will the alarms still be the same
    mark
    Jan 2014
    United Kingdom
    47
    26
    I am confident its a faulty probe according to the manual fault codes but do you have an idea where probe 1 would be situated on this particular chiller.
    Somerset
    63
    4,518
    38
    I can't advise there Mark.
    I don't know that particular chiller.
    Logically it will likely be near the water on or water off (Maybe an insert into the pipes.)
    Check for moisture ingress.
    Some Chillers also have an ambient probe (sitting within the framework sometimes?)
    There are others that know these Chillers better, maybe they can best advise?
    Jan 2014
    United Kingdom
    47
    26
    just to follow up from our conversation. We have found the problem to be lack of oil in one of the compressors. I don't know why it was saying probe 1 error unless it was reading out of the probes set points or limits. possibly low oil pressure.
    thanks for your help.
    Mark
    Somerset
    63
    4,518
    38
    Good to you have had some success Mark.
    Good News is always welcome.