    Question York Screw Chiller How low will it go?????



    I have an interesting problem that perhaps someone can give an answer to.

    A client asked if he could use a York packaged chiller
    (it is the one with the Frick screw mounted ,
    upside down above the chiller I think it is a tdsh 163
    short 200 hp),
    was used for ac water chilling but now he wants to chill
    a salt brine solution to -40 degress F.
    Now before the questions.....
    panel and starter were changed to accomodate the low
    operating conditions, oil cooler was enlarged for the
    extra heat of rejection, and misc other minor changes
    such as a slide valve modify, r-22 is the refrigerant
    Load is approx Xx tons with a flow rate of 450 gpm
    in at -39 F and out at -43 F PD not a problem..
    The system will drain and flush the brine after
    each daily usage to alleviate damage to the copper
    chiller tubes.

    The original capacity was about 200 tons so the 30 or so tons should not be a problem
    I believe there should be ample surface in both the chiller and the condenser to do the new capacity.

    NOW YOU CAN FIRE AWAY. ANY INDUSTRIAL YORK GUYS OUT THERE THAT HAVE USED THIS UNIT FOR REALLY LOW TEMP??

    I really look forward to your comments, This seems to be an excellent one for you Iceman...



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: York Screw Chiller How low will it go?????

    Nothing like a challenge thrown down to get a persons attention...

    a salt brine solution
    • Calcium or sodium chloride???
      • Has anyone checked the material compatibility charts?
      • The system will drain and flush the brine after each daily usage to alleviate damage to the copper chiller tubes.
    I would be concerned about repeated exposure to air, can't say why but this bothers me.




    other minor changes such as a slide valve modify??
    • did this change the Vi?
    with a flow rate of 450 gpm

    in at -39 F (-39.4C) and out at -43 F (-41.6C) PD not a problem..
    • Earlier you mentioned -40F (-40C), which is it?
    • Is the tube velocity high enough to prevent laminar flow??
    • Also, is the brine a liquid mix or flakes?
    For some rough numbers:
    A 163 short (open flash economizer) with R-22 will do about 30 Tons at -50F (-45.5C) suction and 100F (37.7C)condensing (no pressure losses allowed so this is already too low for capacity). Power = 111.3 BHP (~83 kW)

    Without checking further...this looks like it could be trouble...
    Last edited by US Iceman; 23-05-2006 at 02:37 AM. Reason: text formatting

  3. #3
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: York Screw Chiller How low will it go?????

    Iceman

    glad you looked at this, your comments appear "well better then most"......

    The reasons for the questions are for a legal problem of a client and his client.

    The unit was using sodium chloride brine, no flakes.
    The vi (this unit for york, has a fixed vi setting) has been modified to handle the long vi needed
    so the hp - amp draw was below the force unload

    The heat transfer velocity seems to be in the turbulent range my old company was a heat exchanger builder.
    We feel the compatability could be a problem, but if
    drained and flushed as noted it would negate the problem.
    -40 F but -40 c is the same thing .....

    So any more thoughts oh yes we got it to -28 F but the oil temp went high and shut down. They had not changed out the oil cooler at that time.

    best to you..

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: York Screw Chiller How low will it go?????

    The unit was using sodium chloride brine, no flakes.
    The reason I asked about the flakes is that I have seen some problems with tube plugging when the solution is not mixed properly. And/or, shut down for some intervals. If the brine is not mixed correctly and completely, the flakes come out of suspension.

    I have also seen some problems when the chiller tubes are periodically opened to atmosphere. Of course these were carbon steel tubes in ammonia systems, but I'm a little concerned the repeated flushing with clean water may accelerate tube sheet corrosion. Who knows what will happen to the copper tubes.

    The heat transfer velocity seems to be in the turbulent range
    If the copper tubes are enhanced surface the turbulent region for the Reynolds number may have to be higher than prime surface.

    If I remember correctly a Reynolds number at or slightly above 10,000 may not be sufficient to get the most benefit from the tubes.

    we got it to -28 F but the oil temp went high and shut down
    What type of oil cooling are you using? water-cooled PHE??

    If the evaporating temp. is -40C, then you might be able to get away with 30 Tons of cooling capacity if the chiller U value compensates for the lower load. Since the surface area is fixed, I would suspect you can run with a smaller approach temperature to get the 30 Tons.

    The big "maybe" is the film coefficient for the brine. That is the driver.


    The reasons for the questions are for a legal problem of a client and his client.
    That's enough to make the hair on your neck stand-up.

    It sounds like someone said no problem to changing this over to LOW temperature brine, and now they are trying to solve the problems.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: York Screw Chiller How low will it go?????

    I just remembered something else.

    The chiller tubes will be undergoing regular expansion and contraction due to the daily temperature changes. Ambient to very cold, and then warmed up again with the clean water rinse.

    The tube material compatibility may be a secondary issue if the tubes pull out of the tube sheets.

    Normal design practice for an application like this would be to use an expansion joint in the shell.

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: York Screw Chiller How low will it go?????

    Quote Originally Posted by bruceboldy
    tdsh 163 short 200 hp),
    was used for ac water chilling but now he wants to chill
    a salt brine solution to -40 degress F.

    Now before the questions.....
    panel and starter were changed to accomodate the low
    operating conditions
    , oil cooler was enlarged for the
    extra heat of rejection, and misc other minor changes
    such as a slide valve modify, r-22 is the refrigerant
    Load is approx Xx tons with a flow rate of 450 gpm
    in at -39 F and out at -43 F PD not a problem..
    The system will drain and flush the brine after
    each daily usage to alleviate damage to the copper
    chiller tubes.

    The original capacity was about 200 tons so the 30 or so tons should not be a problem
    I believe there should be ample surface in both the chiller and the condenser to do the new capacity.

    NOW YOU CAN FIRE AWAY. ANY INDUSTRIAL YORK GUYS OUT THERE THAT HAVE USED THIS UNIT FOR REALLY LOW TEMP??

    I really look forward to your comments, This seems to be an excellent one for you Iceman...
    This is something hard to understand (for me, please)

    -why to change panel and starter if your Condensing Pressure cP is still 14 bar - problem for motor is not suction but condensing pressure

    -why to enlarge oil cooler if you reduce cooling capacity? -what is extra heat of rejection?

    -what about ECO port

    -what about Vi if you are going to do this in one stage?

    eT= -40C, eP=1.05 bar = 2.05 gauge pressure
    cT= +38C, cP=14,59=14.6 bar = 15.6 bar gauge pressure

    = cP/sP (14.6+1.0/1.049+1.0= 15.6/2.05= Vi=7.60


    -Sodium chloride NaCl (kitchen salt) you can use down to -9C otherways you should use CaCl2/water solution (calcium cloride) down to -45C, but then you have a problem with material (you can use titanium heat exchanger and cast iron or plastic pipes) and not copper type. Definitely system must be flooded becuse CaCL2 is extremely corrosive even to SS material.

    Maybe I miss something

    Best regards,

    Josip
    Attached Images Attached Images
    Last edited by Josip; 23-05-2006 at 09:06 PM. Reason: to add attachment

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: York Screw Chiller How low will it go?????

    josip

    the software in the York panel forces you to change the panel. Once you change the panell you have to change the starter, it is interlocked to the panel.

    The high heat load compression requires the larger oil cooler.

    The Vi was re cut to match the high compression ratio vs simple water cooling.

    Just intersted in the comments of the group about this equipment. and yes the legal comments refer to a money issue ( they always do it seems.

    The tubes are a problem but the flow rate is ok for the new operation. The fluid is cacl2 not sodium chloride as noted earlier. and he was aware of the corrosion concerns.

    Thanks for the intersting observations, and any other comments are welcome, depositions are not for another month!!!!!! Oh yes it was not my idea i am just gathering info...

  8. #8
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    191
    Rep Power
    19

    Wink Re: York Screw Chiller How low will it go?????

    You need 2 stage compressor for this!And R22 isnt best choice too.

    Renato

  9. #9
    Join Date
    Apr 2007
    Location
    Phillipine
    Posts
    22
    Rep Power
    0

    Re: York Screw Chiller How low will it go?????

    Hi,
    Tne Frick screw compressor can go down to -40F only the capcity will be reduced. It has aselection program that compressor can reach these temp. But if it is using a shell and tube it can't because the lowest temp it can reach is -8C(17.6F). you have to replace it with plate heat exchanger so you can put it down to -40F

  10. #10
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    639
    Rep Power
    20

    Re: York Screw Chiller How low will it go?????

    David, when did York start using the code paks (believe that is what they were called) down to -40 dF leaving.

    I'd be concerned with the whole project. I guess you are selling against this if you are still at the same company?

    Corrosion is a real issue and the brine system needs to be pressurized with a nitrogen pad in my opinion.

    I had run across them selling then rated down to about 0 dF leaving and no lower. The compressor can easily run at the conditions noted, but not very efficiently.

    Send me a PM if you can.

    ken

  11. #11
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: York Screw Chiller How low will it go?????

    Sounds like a insurance claim/battle waiting for a court hearing. I would recommend at least a 2 stage ammonia system with a size large flooded PHE evaporator designed for the application, "google" the word Temper as they supply a -40c solution that is half friendly and stable at low temperatures. Legally check your insurances if any advise previously given, failing that change name and leave town.
    Cheers Magoo

  12. #12
    Join Date
    Aug 2007
    Location
    Germany
    Posts
    36
    Rep Power
    0

    Re: York Screw Chiller How low will it go?????

    Most of my concerns about this project are related to the evaporator. -40°F is much below the design temperature of this unit and this can cause huge problems or even injures people. The reason for that is, that the strenght of steel rapidly decreases when the temperature drops to low and this affects integrity of the whole unit. Please refer to the nameplate of pressure vessels before you do something creative to them.

Similar Threads

  1. York Millenium Screw Chiller
    By iceman007 in forum Industrial Compressors
    Replies: 26
    Last Post: 16-01-2011, 12:56 AM
  2. York Chiller
    By HVACGod in forum Commercial
    Replies: 12
    Last Post: 11-09-2010, 06:05 AM
  3. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 03:48 PM
  4. York Open Drive Screw Chiller
    By Cofreth in forum Air Conditioning
    Replies: 4
    Last Post: 24-10-2005, 02:17 PM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 24-03-2004, 12:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •