    Fixed leak detection



    Hello all,
    My first post here.
    Thank you for sharing information and reading my question.
    To comply with the requirements of EN378 and the F GAS regulation sensors must be tested annually.
    Who suppose to do annual calibration of the Fixed leak detection system sniffers?
    We do have a FLD installed, since the systems are quite big > 1000 KG of R 134a.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Fixed leak detection

    Not knowing what the legislation is like in Bulgaria but...

    Annual testing does not normally mean that the sensor(s) needs to be calibrated. Rather that it is logged that someone either used the test button or a "sample leak" and that the leak detection system operated as designed.


  3. #3
    Join Date
    Jun 2006
    Location
    Bulgaria
    Age
    59
    Posts
    5
    Rep Power
    0

    Re: Fixed leak detection

    I believe the regulations in all EU are the same.
    Our regulations stated "Fixed leak detection systems must be checked or calibrated as appropriate at least once every 12 months to ensure proper functioning for stationary refrigeration equipment."
    Is this mean that any certified person can do the 'checks'?

  4. #4
    Join Date
    Jun 2006
    Location
    Bulgaria
    Age
    59
    Posts
    5
    Rep Power
    0

    Re: Fixed leak detection

    Someone please reply.
    Do I have to search for a list of approved vendors to make an annual check, or I can do it by myself?
    What is the practice in the place you are?

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Fixed leak detection

    .

    With most sensors they come with a small bottle that has a waxy
    substance inside it. When this bottle is held near the sensor it
    emits something that triggers the alarm, if the alarm is ok.

    The stuff inside the bottle is specific to a make or a type of refrigerant
    and they emit at levels lower than 5ppm or 5 grammes a year.

    the sensor manufacturer should be able to supply these.

    Rob
    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  6. #6
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Fixed leak detection

    Quote Originally Posted by sailorbg View Post
    Someone please reply.
    Do I have to search for a list of approved vendors to make an annual check, or I can do it by myself?
    What is the practice in the place you are?
    You can do it yourself if you use a calibrated tester to below 5 grammes a year.

    The test would need to be recorded onto the correct documentation.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  7. #7
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16

    Re: Fixed leak detection

    Get a calibrated leak generator such as this http://bit.ly/2uQ541R. Ignore the price in this link.