    Fixed leak detection
    Hello all,
    My first post here.
    Thank you for sharing information and reading my question.
    To comply with the requirements of EN378 and the F GAS regulation sensors must be tested annually.
    Who suppose to do annual calibration of the Fixed leak detection system sniffers?
    We do have a FLD installed, since the systems are quite big > 1000 KG of R 134a.
    Feb 2007
    2,477
    38
    Re: Fixed leak detection
    Not knowing what the legislation is like in Bulgaria but...
    Annual testing does not normally mean that the sensor(s) needs to be calibrated. Rather that it is logged that someone either used the test button or a "sample leak" and that the leak detection system operated as designed.
    Jun 2006
    Bulgaria
    5
    I believe the regulations in all EU are the same.
    Our regulations stated "Fixed leak detection systems must be checked or calibrated as appropriate at least once every 12 months to ensure proper functioning for stationary refrigeration equipment."
    Is this mean that any certified person can do the 'checks'?
    Jun 2006
    Bulgaria
    5
    Someone please reply.
    Do I have to search for a list of approved vendors to make an annual check, or I can do it by myself?
    What is the practice in the place you are?
    May 2012
    1,247
    28
    With most sensors they come with a small bottle that has a waxy
    substance inside it. When this bottle is held near the sensor it
    emits something that triggers the alarm, if the alarm is ok.
    The stuff inside the bottle is specific to a make or a type of refrigerant
    and they emit at levels lower than 5ppm or 5 grammes a year.
    the sensor manufacturer should be able to supply these.
    Rob
    May 2012
    1,247
    28
    Quote Originally Posted by sailorbg View Post
    You can do it yourself if you use a calibrated tester to below 5 grammes a year.
    The test would need to be recorded onto the correct documentation.
    Rob
    Sep 2010
    69
    209
    10
    Get a calibrated leak generator such as this http://bit.ly/2uQ541R. Ignore the price in this link.
    Brian, retired in Devon.