    Feb 2017
    112
    9
    Hitachi condenser not running.
    Hello all, firstly i would like to apologise if this has been asked and answered but i done a search and nothing came up.
    I have been working in a school this past week and there is one class room with issues with the a/c
    i have a wall mount unit model:RAS-35YH6 and the condenser with model: RAC-35YH6 the unit is on R410a.
    The issue is the unit is not calling for cooling, i reset both indoor and outdoor unit and nothing happens, i have 240V at both units and the evaporator unit runs on cooling mode but the condenser never starts up.
    Upon further inspection to the condenser i found that inside the case the unit clicks/ticks for about 3 seconds and then stops.
    Does anyone have any ideas what could be the cause of this? i am back in the school soon to diagnose further but any advice is more than appreciated.
    Thanks in advanced
    Sep 2010
    208
    Re: Hitachi condenser not running.
    Are any of the warning lamps flashing?
    Have you followed the fault finding list?
    Manual here if you need one .... http://bit.ly/2vmneo1
    Brian, retired in Devon.
    Feb 2017
    112
    9
    Hello FaultCode,
    No while i was on site i had no internet access to get the manual, i just downloaded the one you provided, thank you much appreciated.
    Rik
Tags for this Thread