    Daikin cassette 71 split



    Hi we have installed 4 split cassette units 3 work great the 4th does not work the remote control has nothing on it we checked wiring all ok and power to outdoor unit all ok lights are on outdoor unit any ideas please



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Daikin cassette 71 split

    Possibly a faulty remote controller. Try changing it with one that is known to work. Make sure that the interconnecting wiring is making contact in the terminals.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16

    Re: Daikin cassette 71 split

    You say wiring is good but what about voltages at the terminals?
    Brian, retired in Devon.

  4. #4
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin cassette 71 split

    I charge remote few days ago and still blank also voltage is fine

  5. #5
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: Daikin cassette 71 split

    Check the connections at the indoor unit where the controller wires into, usually P1 and P2.
    Had this problem on a Daikin cassette a year ago.
    Turned out to be faulty wiring from the factory. The Forced off wires from the PCB went into the top of where the P1 and P2 terminals were.
    My Controller was blank until I swapped the wires to the right terminals.

    Good luck,
    Keza

  6. #6
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin cassette 71 split

    Thanks Keza I try that on Monday

  7. #7
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin cassette 71 split

    Tried what you said keza no luck

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin cassette 71 split

    Swap the indoor pcb onto a unit you know is working to see if it transfers the fault of runs OK. At least this will tell you if the pcb is at fault or the wiring.

  9. #9
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: Daikin cassette 71 split

    Unlucky mate. Sounds like a PCB problem.
    I would try what Frank suggests.
    Maybe DOA

  10. #10
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin cassette 71 split

    I ordered a new pcb

  11. #11
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: Daikin cassette 71 split

    Let us know how it goes

  12. #12
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin cassette 71 split

    I change the board like Daikin said and still does not work I tried everything

  13. #13
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Daikin cassette 71 split

    Quote Originally Posted by eurocooling View Post
    I change the board like Daikin said and still does not work I tried everything
    What is the voltage at the remote controller cable? You need to check this at the remote controller to prove the cable is okay. Are the LEDs flashing on the indoor PCB? What is the voltage between 2 & 3 on the indoor unit?

  14. #14
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin cassette 71 split

    We have no led flashing and nothing on the remote control this is with new board thanks for your help 2 to 3 there is nothing

  15. #15
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Daikin cassette 71 split

    Quote Originally Posted by eurocooling View Post
    We have no led flashing and nothing on the remote control this is with new board thanks for your help 2 to 3 there is nothing
    Okay you are looking for a DC voltage on 2 to 3 at the indoor and on the remote cable. Can you check 1 to 2 on the indoor you should have AC voltage. Can you check 1 to earth and 2 to earth at the indoor.

    If you don't have AC voltage please go to the outdoor and check 1 to 2 and you should have AC voltage (240v). Also check 2-3 at the outdoor you should have DC voltage.

    If you have voltages on 1,2&3 at the outdoor you a have problem with the cable or spur.

    If you have no voltages on 1,2&3 at the outdoor the glass fuse on the outdoor PCB may have blown.This can be due to a cable issue

    Please post your findings.
    Last edited by Neddy; 21-07-2017 at 06:57 PM.

  16. #16
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin cassette 71 split

    Thank you I will try this

  17. #17
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin cassette 71 split

    What is the full model number of the outdoor unit?

  18. #18
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin cassette 71 split

    Sorted it now we had a faulty outdoor board all working