Results 1 to 18 of 18
    Feb 2008
    Portugal
    47
    201
    11
    Daikin cassette 71 split
    Hi we have installed 4 split cassette units 3 work great the 4th does not work the remote control has nothing on it we checked wiring all ok and power to outdoor unit all ok lights are on outdoor unit any ideas please
    Dec 2008
    511
    Re: Daikin cassette 71 split
    Possibly a faulty remote controller. Try changing it with one that is known to work. Make sure that the interconnecting wiring is making contact in the terminals.
    Sep 2010
    70
    209
    10
    You say wiring is good but what about voltages at the terminals?
    Brian, retired in Devon.
    Feb 2008
    Portugal
    47
    201
    11
    I charge remote few days ago and still blank also voltage is fine
    Aug 2014
    Australia
    30
    68
    4
    Check the connections at the indoor unit where the controller wires into, usually P1 and P2.
    Had this problem on a Daikin cassette a year ago.
    Turned out to be faulty wiring from the factory. The Forced off wires from the PCB went into the top of where the P1 and P2 terminals were.
    My Controller was blank until I swapped the wires to the right terminals.
    Good luck,
    Keza
    Feb 2008
    Portugal
    47
    201
    11
    Thanks Keza I try that on Monday
    Feb 2008
    Portugal
    47
    201
    11
    Tried what you said keza no luck
    Oct 2001
    Nottingham UK
    5,127
    42
    Swap the indoor pcb onto a unit you know is working to see if it transfers the fault of runs OK. At least this will tell you if the pcb is at fault or the wiring.
    I'm back on the Pale
    Aug 2014
    Australia
    30
    68
    4
    Unlucky mate. Sounds like a PCB problem.
    I would try what Frank suggests.
    Maybe DOA
    Feb 2008
    Portugal
    47
    201
    11
    I ordered a new pcb
    Aug 2014
    Australia
    30
    68
    4
    Let us know how it goes
    Feb 2008
    Portugal
    47
    201
    11
    I change the board like Daikin said and still does not work I tried everything
    Mar 2009
    Uk
    36
    121
    11
    Quote Originally Posted by eurocooling View Post
    What is the voltage at the remote controller cable? You need to check this at the remote controller to prove the cable is okay. Are the LEDs flashing on the indoor PCB? What is the voltage between 2 & 3 on the indoor unit?
    Feb 2008
    Portugal
    47
    201
    11
    We have no led flashing and nothing on the remote control this is with new board thanks for your help 2 to 3 there is nothing
    Mar 2009
    Uk
    36
    121
    11
    Okay you are looking for a DC voltage on 2 to 3 at the indoor and on the remote cable. Can you check 1 to 2 on the indoor you should have AC voltage. Can you check 1 to earth and 2 to earth at the indoor.
    If you don't have AC voltage please go to the outdoor and check 1 to 2 and you should have AC voltage (240v). Also check 2-3 at the outdoor you should have DC voltage.
    If you have voltages on 1,2&3 at the outdoor you a have problem with the cable or spur.
    If you have no voltages on 1,2&3 at the outdoor the glass fuse on the outdoor PCB may have blown.This can be due to a cable issue
    Please post your findings.
    Feb 2008
    Portugal
    47
    201
    11
    Thank you I will try this
    Oct 2001
    Nottingham UK
    5,127
    42
    What is the full model number of the outdoor unit?
    Feb 2008
    Portugal
    47
    201
    11
    Sorted it now we had a faulty outdoor board all working