    Unhappy R412A refrigerant gas. Help me!!!



    Dear Friends:

    I needs to buy a R412A gas refrigerant. I have a low temerature freezer (-80ēC), with two stages. A low compressor is dead, and i needs to change a compressor. But the big problem, is i cannot to found a R412 buyer!!!. Please, can you tell me where i can to buy it refrigerant or a replacement?. Which is the appropiate oil to use?. Thanks your very much, i needs this information urgently. I apologize my english please.



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: R412A refrigerant gas. Help me!!!

    Can you not recover the gas as this will be needed no matter what, Use a couple new filter dryers to clean the gas as it comes into the tank, then once replaced of the dead one refill with your gas?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: R412A refrigerant gas. Help me!!!

    Have a look also at this thread....
    http://www.refrigeration-engineer.co...ead.php?t=4097
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    maha25's Avatar
    maha25 Guest

    Re: R412A refrigerant gas. Help me!!!

    Quote Originally Posted by patrickjota View Post
    Dear Friends:

    I needs to buy a R412A gas refrigerant. I have a low temerature freezer (-80ēC), with two stages. A low compressor is dead, and i needs to change a compressor. But the big problem, is i cannot to found a R412 buyer!!!. Please, can you tell me where i can to buy it refrigerant or a replacement?. Which is the appropiate oil to use?. Thanks your very much, i needs this information urgently. I apologize my english please.

  5. #5
    Join Date
    Jun 2007
    Location
    Norway
    Age
    74
    Posts
    56
    Rep Power
    17

    Re: R412A refrigerant gas. Help me!!!

    Hi Patrickjota.

    If it is the low stage/second stage is is weird if the gas should be R412A. That one has a boiling point of just -38,1c at abs.1bar If the maker use an Asian made ICI the label could say TP5R and that is R412A. If the label tells TP5R3, it is the low temperature gas 508A. If so, you could use 508B. If it is the high stage/first stage, the R412A could be the one you are looking for. ICI use the name Arcton for the TP seriesI forgot to tell.
    Pedro

Similar Threads

  1. R600 Refrigerant.
    By tonydeith in forum Refrigerants
    Replies: 14
    Last Post: 21-04-2011, 08:52 AM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. Replies: 2
    Last Post: 16-11-2005, 05:34 PM
  4. Liquid refrigerant and bubles in sightglass
    By aygul in forum Trouble Shooting
    Replies: 2
    Last Post: 30-08-2003, 09:07 PM
  5. Refrigerant Reclamation
    By herefishy in forum Commercial
    Replies: 6
    Last Post: 23-07-2003, 08:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •