Results 1 to 11 of 11
    Sep 2016
    Brazil
    27
    Fans shutdown sequence in evaporative condensers
    What is the best fans shutdown sequence in evaporative condensers?
    I have 3 condensers with 12 fans each and more 2 condensers with 8 fans each.
    Tks, Renata
    2,533
    28
    Re: Fans shutdown sequence in evaporative condensers
    Could you please tell us what type or style of condenser & fans.
    If you turn fan/s off is fan/s sectioned off so they don't run backwards or short circuit air.
    The most effective way for power savings is to have VSD on all fans rampining up & downs together with a common set point in most cases. Very smooth operation can be achieved.
    Sep 2010
    70
    209
    10
    From a previous thread on this subject my reply was.....
    Found this semi-sales literature which explains methods and reasons of fan control...
    http://bit.ly/2sg8cBI
    Brian, retired in Devon.
    Sep 2016
    Brazil
    27
    Hello Hanger1, you can see the fans and condenser in these pictures:
    Very nice post, FaultCode, it will help! For sure!
    2,533
    28
    Renata,
    So installing a VSD on all fans a possibility?
    Save power, smooth operation.
    Sep 2016
    Brazil
    27
    Ranger1,
    I agree with you, but those evaporative condensers will be replace soon, then I just want to get better performance I can without invest much money.
    Aug 2014
    69
    427
    Hi Renata
    The liquid outlet connection is the most important part of any condenser. The liquid exiting the condenser must always have the coldest air blowing around it to gain as much subcooling as possible. So the fans furthest away from the liquid outlet go off first and the fans nearest the liquid outlet go off last this will guarantee the best subcooling possible
    Sep 2008
    Canada
    770
    12
    Hi, Glen.
    I think that it is misunderstanding. You and FaultCode mentioned about air condensers, but Renata asked about evaporative condensers which typically use for industrial refrigeration. Evaporative condensers wetted by water and sequence of condenser fans is not so important. Water works as "flywheel" and pressure differential can be as low as 10-15 psig. Properly designed and installed evaporative condensers should not have subcooling at outlet. I think that not so much condenser fan sequence is important but right condenser pressure set point should chosen. Sometimes condensing pressure can float but benefits of floating are not significant.
    Aug 2014
    69
    427
    Segei
    Your right but the picture of the condenser is looks like a multi fan condenser but I may be wrong as the picture is not clear on my phone!?
    Sep 2008
    Canada
    770
    12
    From the top it looks like air condenser. From the side it looks like evaporative condenser. I'm not familiar with these condensers.
    Sep 2016
    Brazil
    27
    Hello every one,
    I've decided to invest in VSD, I believe it is the best option.
    Thanks,
    Renata