Results 1 to 6 of 6
  1. #1
    Join Date
    Feb 2016
    Location
    Uk
    Age
    48
    Posts
    48
    Rep Power
    0

    Wiring a sauter actuator



    I need help wiring an actuator from a controller board that has 3 wires
    On the photo wiring diagram it is 25,26 and 27
    Thanks in advanceIMG_4675.jpg
    Attached Images Attached Images



  2. #2
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    75
    Posts
    209
    Rep Power
    16

    Re: Wiring a sauter actuator

    Which actuator do you have? Little clues make thing easier

  3. #3
    Join Date
    Feb 2016
    Location
    Uk
    Age
    48
    Posts
    48
    Rep Power
    0

    Re: Wiring a sauter actuator

    Quote Originally Posted by FaultCode View Post
    Which actuator do you have? Little clues make thing easier
    Sorry mate
    It's the adm322sf152
    I have 3 wires coming from a rycroft controller board for a hot water heat exchanger they are labelled 25,26 and 27 on the wiring diagram and in the actuator I have mm then 1-6

  4. #4
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    75
    Posts
    209
    Rep Power
    16

    Re: Wiring a sauter actuator

    Is it a 2 port or 3 port valve and do you have any other controls in line with it, i.e. open or close commands.

    [Edit] Checking the drawings again I reckon you need scheme 5a but without the feedback loop, so---->

    Controller - function - actuator

    25 - 2-10v signal - 03
    26 - 0 volts - MM
    27 - 24 volts - 01
    Last edited by FaultCode; 24-06-2017 at 11:48 PM.

  5. #5
    Join Date
    Feb 2016
    Location
    Uk
    Age
    48
    Posts
    48
    Rep Power
    0

    Re: Wiring a sauter actuator

    Quote Originally Posted by FaultCode View Post
    Is it a 2 port or 3 port valve and do you have any other controls in line with it, i.e. open or close commands.

    [Edit] Checking the drawings again I reckon you need scheme 5a but without the feedback loop, so---->

    Controller - function - actuator

    25 - 2-10v signal - 03
    26 - 0 volts - MM
    27 - 24 volts - 01
    Many thanks mate
    Going there tomorrow so will give it a try
    It is just manually fully open at the moment
    Will let you know how I get on.

  6. #6
    Join Date
    Aug 2017
    Location
    United Kingdom
    Posts
    7
    Rep Power
    0

    Re: Wiring a sauter actuator

    Should have gone for a Belimo ..