    Feb 2016
    Uk
    43
    40
    Wiring a sauter actuator
    I need help wiring an actuator from a controller board that has 3 wires
    On the photo wiring diagram it is 25,26 and 27
    Sep 2010
    70
    209
    11
    Re: Wiring a sauter actuator
    Which actuator do you have? Little clues make thing easier
    Feb 2016
    Uk
    43
    40
    Quote Originally Posted by FaultCode View Post
    Sorry mate
    It's the adm322sf152
    I have 3 wires coming from a rycroft controller board for a hot water heat exchanger they are labelled 25,26 and 27 on the wiring diagram and in the actuator I have mm then 1-6
    Sep 2010
    70
    209
    11
    Is it a 2 port or 3 port valve and do you have any other controls in line with it, i.e. open or close commands.
    [Edit] Checking the drawings again I reckon you need scheme 5a but without the feedback loop, so---->
    Controller - function - actuator
    25 - 2-10v signal - 03
    26 - 0 volts - MM
    27 - 24 volts - 01
    Feb 2016
    Uk
    43
    40
    26 - 0 volts - MM
    27 - 24 volts - 01
    Many thanks mate
    Going there tomorrow so will give it a try
    It is just manually fully open at the moment
    Will let you know how I get on.
    Aug 2017
    United Kingdom
    3
    Should have gone for a Belimo ..