Results 1 to 8 of 8
  1. #1
    Join Date
    Dec 2011
    Location
    spain
    Age
    63
    Posts
    42
    Rep Power
    0

    Inverter not cooling. Gas seems right



    I was called out to look at a "budget" inverter unit MovAir 12k Btu that wasn't cooling at all. The unit had no gas and outdoor unit had an obstruction in front of it. Found the leak, regassed and everything else looked fine including the service valves sweating. I thought job done, just check on indoor unit and it works 'a bit' with room temp at 27c and indoor unit only producing 22c. Everything seems cleanish. I seem to remember there was a limit could get the temp down when it was also hot outside. Could that be the case?



  2. #2
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    208
    Rep Power
    16

    Re: Inverter not cooling. Gas seems right

    Yes, it depends on the unit specification as to what the operating results are.

  3. #3
    Join Date
    Feb 2006
    Location
    Hampshire
    Posts
    61
    Rep Power
    19

    Re: Inverter not cooling. Gas seems right

    Room at 27 and air off at 22 is not right at all.
    What were the operating pressures? Was the correct charge weighed in?

  4. #4
    Join Date
    Dec 2011
    Location
    spain
    Age
    63
    Posts
    42
    Rep Power
    0

    Re: Inverter not cooling. Gas seems right

    Sorry for the delay in replying, ironically the heat has taken it's toll on me and I had to stop work for a few days. R410a operating pressure was 100 psi, with Air Con running on full cooling. I watched the service valves start from nothing to frost and then to sweating. I didn't weigh the load in, but never had to in the past. Just to clarify, the outdoor unit is on a roof and temp is probably 36c, the lowest I can get the indoor unit is 22c.

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Inverter not cooling. Gas seems right

    Quote Originally Posted by rubybree View Post
    I didn't weigh the load in, but never had to in the past.
    OK, Good luck in finding the issue(s).


    Slowly shakes ones head and walk away in to the sunset....

  6. #6
    Join Date
    Dec 2011
    Location
    spain
    Age
    63
    Posts
    42
    Rep Power
    0

    Re: Inverter not cooling. Gas seems right

    Thanks for the advice Viking, as I didn't install it and it was a cheap supermarket unit anyway, I did walk away from it in the end.

  7. #7
    Join Date
    Oct 2013
    Location
    Australia
    Posts
    45
    Rep Power
    0

    Re: Inverter not cooling. Gas seems right

    Mate it's most likely got to do with the charge.
    If it's an inverter unit you can't really guess the charge in.
    I'd say it's actually low on gas.

  8. #8
    Join Date
    Dec 2011
    Location
    spain
    Age
    63
    Posts
    42
    Rep Power
    0

    Re: Inverter not cooling. Gas seems right

    Thanks for the info Sparkletron.

Posting Permissions