Thread: the subcooling and superheat
20-06-2017, 09:18 AM #1
the chiller composed by a screw compressor, a water-cooled shell-and-tube condenser, a thermal expansion valve and a dry-expansion shell-and-tube evaporator, from the ARI 550/590-98, the standard inlet and outlet cooling temperature are 85F and 95F, the chilled water ranged from 54F to 44F. then I have some questions as follow:
(1) what should be appropriate sub-cooling for this style of unit?
(2) what should be appropriate approach for the DX shell-and-tube evaporator?
(3) what should be the super-heat values for the evaporator and the system(super-heat of suction line)
in addition, the approach for flooded evaporator is
Approach_flooded=Tout_chilled_water-Tsat, but DX shell-and-tube evaporator always equipped an external balance thermal expansion valve, so how to define the approach of DX evaporators. in my mind, Approach_DX=Tout_chilled_water-Tout_refrigerant, where Tout_refrigerant is the actual refrigerant outlet temperature of the DX evaporator, I don't know is it correct.Last edited by trace; 20-06-2017 at 11:01 AM.
21-06-2017, 09:38 AM #2
Re: the subcooling and superheat
23-06-2017, 02:18 AM #3
Thanks moideen for your reply. The saturated suction temperature is decided by the boiling pressure and the pressure drops of the DX evaporator, since the pressure drops is not a constant for different manufacturer, the LTD must vary in a certain range, I wonder the LTD range.