Thread: Sequence of fan
    Mar 2016
    IRAN
    165
    3
    Sequence of fan
    Dear Friends,
    I have a question.
    Suppose that we have an air-cooled condenser with 8 fans and we want to control discharge pressure by turning on/off condenser fans by pressure switch.
    In this case for turning on or off sequence of fans are important ? or it is not important witch fan should be first or second or third one ?
    Sincerely yours.
    Apr 2008
    Southampton, England
    44
    933
    29
    Re: Sequence of fan
    Looking at two fan systems it seems normal to have the fan near the condenser outlet to stay on and cycle the other one. Theory being the refrigerant leaving the coil might heat up a bit if you cycle the other fan or liquid might sit by the inlet to the condenser (so I've been told).
    Saying that, AC with an inverter pack will keep the top fan running to cool the PCB and cycle the lower fan so kind of blows that theory out the water a bit.
    So, for the purist fans near the outlet on, fan near the inlet cycled.
    Cheers,
    Andy.
    Sep 2010
    70
    209
    11
    Re: Sequence of fan
    Found this semi-sales literature which explains methods and reasons of fan control...
    http://bit.ly/2sg8cBI
    Without arguing with Tayters this paper suggests keeping the fans at the inlet running to prevent thermal shock on the tubing.
    Mar 2016
    IRAN
    165
    3
    Re: Sequence of fan
    Quote Originally Posted by FaultCode View Post
    Dear Faultcode,
    Thanks form your and Tayters help.
    I will read your literature and will say my opinion.
    Sincerely yours.