    High % RLA (about 400%) of compressor motor at start-up



    Dear forum fellows;

    We have TRANE chiller RTWA-216 and one of its motor is having high RLA (about 400% ~ 700 A ) at start-up followed by breaker trip.
    It is worthy to mention that in last season it operated normally .Motor Megger results are also not bad.

    It remained shut-down for many months and the only work that has recently been done is replacement of its cable from main panel.

    Please guide what possible reasons may be and how to troubleshoot it.

    Thanks in advance



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: High % RLA (about 400%) of compressor motor at start-up

    Hi.
    Is it possible the motor has got Damp?
    Sometimes warming the motor to dry off any Moisture absorbed whilst standing idle, will resolve a tripping motor.
    You say Megga readings are not Bad?
    Care to elaborate?
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  3. #3
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: High % RLA (about 400%) of compressor motor at start-up

    Quote Originally Posted by Grizzly View Post
    Hi.
    Is it possible the motor has got Damp?
    Sometimes warming the motor to dry off any Moisture absorbed whilst standing idle, will resolve a tripping motor.
    You say Megga readings are not Bad?
    Care to elaborate?
    Grizzly
    Every time compressor heaters have been run for sufficient time before getting motor started. I wanted to say that motor insulation resistance values /Meggering results are greater than 700 K ohms.

    what are possibilities of mechanical seizure of compressor ?

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: High % RLA (about 400%) of compressor motor at start-up

    Is there only one compressor having an issue? If not i would look at the new cable...
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: High % RLA (about 400%) of compressor motor at start-up

    Hi
    You say the mega results are greater than 700 k ohms. What test voltage did you use, 500 or 1000?
    I would normally say anything below 2 megohm would be suspect and as Al suggested the cables could be at fault.
    We are presuming you meggered from the board, if so disconnect at the motor and redo, this should confirm whether it is motor or cable.
    Regards
    Paul
    Born to fish, forced to work

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: High % RLA (about 400%) of compressor motor at start-up

    Assuming a screw compressor
    Was it direction tested after new cable was installed?
    If so how & by whom.
    If not it could be at risk.
    Is it at minimum load?

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: High % RLA (about 400%) of compressor motor at start-up

    Single phasing for some reason?

  8. #8
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    15

    Re: High % RLA (about 400%) of compressor motor at start-up

    Is 700A real amps or reading on display?

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: High % RLA (about 400%) of compressor motor at start-up

    Typical result for a phase lost.
    Check motor protector and contactor. At such high amps, they both need replacing.