Daikin Concealed twin split power
Hi, do concealed fan coils in a twin split system require independent mains power?
or can you link across from the 1&2 terminals?
-
03-06-2017, 08:09 PM #2
Re: Daikin Concealed twin split power
If being powered from a separate feed and as long as there is a local isolator to each one you will be okay.
If being fed from the condensing unit then check with the installation instructions. Separate local isolators still required.Last edited by FaultCode; 03-06-2017 at 08:13 PM.
-
03-06-2017, 08:39 PM #3
Re: Daikin Concealed twin split power
if you look at the inside of the electrical box cover (indoor unit) it shows a 'common connection' with links across from 1 & 2 terminal numbers
-
03-06-2017, 10:16 PM #4
Re: Daikin Concealed twin split power
normally you link from outdoor to 1st spur then out to 2nd spur- ensuring your comms s3 or no 3 is thru crimped- whats the model number ?