    Daikin Concealed twin split power



    Hi, do concealed fan coils in a twin split system require independent mains power?
    or can you link across from the 1&2 terminals?



  2. #2
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16

    Re: Daikin Concealed twin split power

    If being powered from a separate feed and as long as there is a local isolator to each one you will be okay.

    If being fed from the condensing unit then check with the installation instructions. Separate local isolators still required.
    Last edited by FaultCode; 03-06-2017 at 08:13 PM.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin Concealed twin split power

    if you look at the inside of the electrical box cover (indoor unit) it shows a 'common connection' with links across from 1 & 2 terminal numbers

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin Concealed twin split power

    normally you link from outdoor to 1st spur then out to 2nd spur- ensuring your comms s3 or no 3 is thru crimped- whats the model number ?