    Closed economizer control



    Hello everybody,

    I would like to know the best way, in your opinion, to control a closed economizer (subcooler). Follows data from the currently installed system that we would like to improve:

    The existing liquid subcooling system has 2 shell and tube heat exchangers (closed economizer).
    Each of the low-temperature circuit compressors has an intermediate suction port to meet each of the economizers.
    These exchangers are supplied with liquid ammonia from the liquid container and have thermostatic expansion valves for reducing and controlling the evaporator pressure of the exchanger.
    The sub-cooled liquid supplies one URL.
    The construction project of the exchanger is not available.

    tks



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Closed economizer control

    Renata,
    What would you like to know exactly?
    Is this a single stage system, or 2 stage system, can you explain it more?
    Normally you would turn liquid off to economiser heat exchanger when compressor in unloaded condition as it goes to suction at that point, say 70%.
    Best to have modulating valve on liquid being subcooled for smooth constant operation of economiser.

  3. #3
    Join Date
    Sep 2016
    Location
    Brazil
    Posts
    27
    Rep Power
    0

    Re: Closed economizer control

    Hi Ranger1,

    I am sending a figure with the configuration of the system.
    I want to change the thermostatic valve by a eletronic expansion valve, mainly because I want to monitor the ECO remotely.

    Croqui.png
    tks, Renata

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Closed economizer control

    Renata,
    Usually use pulsing valve for this like Danfoss AKVA electronic valve.
    Also not required to work until compressor close to full load.

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Closed economizer control

    Liquid supply to the economizer should be turned of at capacity 70-80%. However, slide valve should be calibrated properly. For example. When slide valve is 100%, el. motor load is 100% as well. Start manually unload compressor. Motor load goes down but slide valve still 100%. When motor load is 80%, slide valve capacity start going down. Saw it many times. During manual unloading slide valve capacity and motor load should start moving simultaneously. However, rate of reduction will be different.

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Closed economizer control

    Quote Originally Posted by Segei View Post
    Liquid supply to the economizer should be turned of at capacity 70-80%. However, slide valve should be calibrated properly. For example. When slide valve is 100%, el. motor load is 100% as well. Start manually unload compressor. Motor load goes down but slide valve still 100%. When motor load is 80%, slide valve capacity start going down. Saw it many times. During manual unloading slide valve capacity and motor load should start moving simultaneously. However, rate of reduction will be different.
    Don't know if I understand this Segei.
    Are you referring to a particular brand compressor?
    Can you give example.

    Thanks

  7. #7
    Join Date
    Sep 2016
    Location
    Brazil
    Posts
    27
    Rep Power
    0

    Re: Closed economizer control

    Ranger1,
    The electronic valve will operate to maintain the superheat at the economizer, is it right?
    Is there any optimum superheat set point?
    tks, Renata

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Closed economizer control

    Quote Originally Posted by Renata View Post
    Ranger1,
    The electronic valve will operate to maintain the superheat at the economizer, is it right?
    Is there any optimum superheat set point?
    tks, Renata
    Well normally suction line just out of heat exchanger is where to sense superheat to get best response.
    Worst case you would get a bit of a flood back which always best to avoid if possible.
    If superheat to high, poorer performance, if to low potential floodback.
    I would have thought 6-8k of superheat, but if electronic it will work itself out to be able to control.
    Like I mentioned earlier, a constant flow through heat exchanger will give best results so things can stabilize.
    If on off, expect average results.

    What type of valve exactly are you going to use on heat exchanger?

  9. #9
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Closed economizer control

    Frick compressors have this issue.

  10. #10
    Join Date
    Sep 2016
    Location
    Brazil
    Posts
    27
    Rep Power
    0

    Re: Closed economizer control

    Propably I will use a Danfoss AKVA.