    Discharge pressure of ammonia compressor
    How many psi maximum discharge pressure of reciprocating compressor
    Sep 2010
    208
    Re: Discharge pressure of ammonia compressor
    Make and model number of compressor required before that can be answered.
    Check manufacturers data sheet.
    Sep 2009
    Iran
    66
    672
    1
    it depends on our condensing temp.
    normally every company has own test pressure for that
    3,356
    Maximum discharge pressure if system is designed correctly is 10-15% below lowest relief valve setting on high side of plant.
    Relief valve should have been selected by looking at maximum design pressure on each pressure vessel or component.
    Have a look at reliefs on compressor, high pressure liquid receiver & whatever in on high side.
    What ever is lowest setting based on that you high pressure switch should be minimum 10% below that.
    Sep 2008
    Canada
    811
    Compression ratio should not be greater than 8:1.
    Jun 2014
    india
    30
    Thanks you friends