    Ammonia refrigerant leval



    How much sufficient level of ammonia in receiver



  2. #2
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    75
    Posts
    209
    Rep Power
    16

    Re: Ammonia refrigerant leval

    Correct amount.

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Ammonia refrigerant leval

    Hi

    Amount of refrigeration in receiver ? Receiver is covering our unbalancing liquid in system when our system is working and also separating liquid from gas and we have only liquid in the pipe ( in NH3 or ***** )

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Ammonia refrigerant leval

    Maximum level in liquid receiver is 80% so if pressure relief valve was to vent, would vent gas, not liquid.
    If level to high liquid can bank up in condenser causing high discharge pressures.

  5. #5
    Join Date
    Jun 2014
    Location
    india
    Age
    30
    Posts
    23
    Rep Power
    0

    Re: Ammonia refrigerant leval

    Ranger Sir..... How much minimum level of liquid in ammonia receiver

  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Ammonia refrigerant leval

    Hi
    Min. is no gas should charge from receiver to separator .and all should be liquid
    normally about 1/3 of D separator .

  7. #7
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Ammonia refrigerant leval

    Quote Originally Posted by manmohan View Post
    Ranger Sir..... How much minimum level of liquid in ammonia receiver
    if your receiver only feeds liquid to consumers (evaporators), and there is no liquid needed for LRI for compressors or thermo syphon oil cooling, it is very easy...

    the level needs to be high enough so that you are sure that the evaporators are being fed with liquid.

    I don't know how large your receiver is, or how you are measuring the level.

    From experience, the level should be around 15% to make sure that the liquid line is fed with pure liquid, if it is a horizontal receiver.

    see attached drawing:
    level.jpg
    -Cheers-

    Tycho

  8. #8
    Join Date
    Jun 2014
    Location
    india
    Age
    30
    Posts
    23
    Rep Power
    0

    Re: Ammonia refrigerant leval

    Thank you very much sir for explain but my liquid outlet from top to receiver and that's mounted horizontal position . I think 50℅ level in Level glass is Best According to your .

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Ammonia refrigerant leval

    Quote Originally Posted by manmohan View Post
    Thank you very much sir for explain but my liquid outlet from top to receiver and that's mounted horizontal position . I think 50℅ level in Level glass is Best According to your .
    Liquid line from top of liquid receiver usually goes down close to bottom of vessel & is cut at a 45 degree angle.
    So shell of liquid receiver is say 20 mm thick, then add diameter of liquid line, say 50mm, allow 25mm for liquid line not quite touching bottom of vessel.
    That is minimum level before liquid line would allow gas into it, so you still need to add more for minimum level.
    If unlucky have seen liquid line dip pipes no where near bottom so upsets results.
    Some people get confused by sight glass, that is why measure off bottom of receiver to get accurate result, then mark it so minimum is known.
    Level probes if used could be indicating different level than actual level as well.

    I think if all measures ok 20-25% level under plant full load.

    If you have liquid injection oil cooling maybe more!

  10. #10
    Join Date
    Jun 2014
    Location
    india
    Age
    30
    Posts
    23
    Rep Power
    0

    Re: Ammonia refrigerant leval

    Ranger Sir.....Thank you so much for your comments

  11. #11
    Join Date
    Apr 2016
    Location
    UK
    Age
    65
    Posts
    7
    Rep Power
    0

    Re: Ammonia refrigerant leval

    what sort of level control do you have on the evaporator? is it a High Side Float , a low side float , a Danfoss PM type valve with level controller, on some ammonia systems with a critical charge and a high side float you may not have a level in the receiver except when you pump the system down.