    Trane chiller Rtaa 324 - display no communicatio



    Hi all,
    Trane chiller model RTAA 324
    Shutdown for maintenance after completing job restored the power found display showing (adaptive control )
    No Communication, No Valid Data.
    Checked voltages and signals on the comms modules also checked fuses all seemed ok. Has anyone experienced this problem.

    Kindly advice to fix the above



  2. #2
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: Trane chiller Rtaa 324 - display no communicatio

    Hi Anish,
    If wiring, voltage and communication cables are OK and red leds (receive – transmit) on the back of the display module are not blink, then most probably the main module A1 is dead.
    Regards,
    CV

  3. #3
    Join Date
    May 2008
    Location
    uae
    Age
    44
    Posts
    40
    Rep Power
    0

    Re: Trane chiller Rtaa 324 - display no communicatio

    The main module A1 can be repaired or to be replaced by new one..