15-05-2017, 12:36 PM #1
old R410a pipework with a new R32 split
Hi, I've got a dead MHI split on R410a, can i use install a new R32 split onto the pipework without using a flushing agent? New Fuj is same size. Pipe is buried in a wall. Fault was fan motor and PCB not burn out. My quote will be nuts is a need to replace the pipe! Cheers
15-05-2017, 12:56 PM #2
Re: old R410a pipework with a new R32 split
Dry nitrogen first and then use the same tubes ......
15-05-2017, 08:08 PM #3
same pipework if its a 410a system
http://www.daikintech.co.uk/Data/Blu...219-371844.pdf
16-05-2017, 04:10 AM #4
I wouldn't have an issue with it. I call it "rounding the corners" not "cutting the corners"
Needs must.
16-05-2017, 12:43 PM #5
I know the pipe size etc is good, i'm thinking oil problems?
16-05-2017, 03:11 PM #6
As mentioned above, dry nitrogen purge to remove any remaining oil etc. As R410A is made up of 50% R32, there should not be an oil compatibility or return problem.
27-06-2017, 12:38 PM #7
Blast it out with nitro and it'll be fine.
If it's not a burn out, your pretty safe.
Mhi 410 models run polyolester oil, I'm certain Fujitsu r32 is the same.