    old R410a pipework with a new R32 split
    Hi, I've got a dead MHI split on R410a, can i use install a new R32 split onto the pipework without using a flushing agent? New Fuj is same size. Pipe is buried in a wall. Fault was fan motor and PCB not burn out. My quote will be nuts is a need to replace the pipe! Cheers
    Dec 2010
    Greece
    181
    14
    Re: old R410a pipework with a new R32 split
    Dry nitrogen first and then use the same tubes ......
    Oct 2007
    manchester
    5,639
    45
    same pipework if its a 410a system
    http://www.daikintech.co.uk/Data/Blu...219-371844.pdf
    Aug 2008
    Auckland
    55
    259
    21
    I wouldn't have an issue with it. I call it "rounding the corners" not "cutting the corners"
    Needs must.
    May 2017
    Australia
    7
    I know the pipe size etc is good, i'm thinking oil problems?
    Dec 2008
    564
    As mentioned above, dry nitrogen purge to remove any remaining oil etc. As R410A is made up of 50% R32, there should not be an oil compatibility or return problem.
    Bedford. Now retired and trying to relax.
    Oct 2013
    Australia
    45
    Blast it out with nitro and it'll be fine.
    If it's not a burn out, your pretty safe.
    Mhi 410 models run polyolester oil, I'm certain Fujitsu r32 is the same.