    An Inspired Mod.



    Hi Guys!
    Attached are some pics of an Idea my colleague came up with this week.
    As I have posted before We look after a large Cold Store, where the Defrost drainline design is "Cr*p!"!
    Resulting in frequent ice build up which will creep along the s/steel pipes. Eventually blowing the
    Rodding eye cap off through its retaining ring.
    Such is the force of growing Ice!

    After several failures the blanking cap is quite badly distorted.
    "Lets make a plastic blank!" was the suggestion.
    This is what Freddie came up with!

    20170511_111821.jpg20170511_115907.jpgWP_20161128_001.jpg



    Brilliant.
    Complete with Ice build up indicator!
    Grizzly


    Despite the High Cost of Living it still remains Popular!

  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: An Inspired Mod.

    .

    Sometimes the simple solution is the best

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: An Inspired Mod.

    Good engineers will always come up with the simplest solutions, Well done . Would not fancy defrosting that drain though haha .

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: An Inspired Mod.

    Hi Guys!
    Thanks for responding.
    In answer Joe to your comment about defrosting that frozen drainline.
    We have become quite good at clearing them using a £20.00 240v steam stripper.

    If you remove the steam tray and use the flexible hose as a steam lance.
    You can literally blast through the Ice.
    It can still take the best part of a day to clear though.
    Cheers Grizzly
    Despite the High Cost of Living it still remains Popular!

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: An Inspired Mod.

    Hi Grizzly,
    Drain lines are a pain.
    I always insert a flexible heater inside them, connected to the main defrost heaters and it does wonders.

    Check it here: http://www.flexelec.com/products/hea...rs-t-rs-i.html

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: An Inspired Mod.

    Sorry Chemi
    We are removing the flexible Heater tapes that were specified by the consultant,
    To run down the inside of the drainline's..
    Because of the operating parameters and the poorly designed defrost system.
    You end up with a Polo Mint down the drains at best.
    At worst the heater tape fails and the sediment from the coolers builds up around them.

    If I was allowed I would spiral wind the tapes around the outside of the pipes.
    Plus move the vapour seal to just outside the pod , not at ground level outside the store approx. 40 metres away!
    Trust Me! We have tried every option and in this scenario internal Heater tapes do not work!
    Cheers Grizzly
    Last edited by Grizzly; 14-05-2017 at 10:08 PM.
    Despite the High Cost of Living it still remains Popular!

  7. #7
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: An Inspired Mod.

    Me I always try to get the drain lines out of the room in the shortest way and in the largest bore tube,but I power the heaters on a permanent basis whether it's internal or external,on a large cold store where multiple evaporator are in action I find it the best way?