    Hey guys, I just want to run this up the flag pole before doing it.

    I'm stuck between concerns about oil return, and not wanting refrigerant running down towards the compressor during the off cycle. Or maybe even oil for that matter?



    Do I want pitch on the horizontal run as I assumed, or will this tend to cause slugging on startup?
    Attached Images Attached Images
    Last edited by MrTube; 25-04-2017 at 02:23 PM.



  2. #2
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16

    Re: Lineset considerations for oil return etc

    A good pipeline design guide by Mcquay may help.....

    https://www.google.co.uk/url?sa=t&so...I-8dNyqzMwexMg

  3. #3
    Join Date
    Apr 2017
    Location
    Canada
    Posts
    1
    Rep Power
    0

    Re: Lineset considerations for oil return etc

    I was always told inverted trao right at vertical drop and if off on cycles are far apart then at the very least a compressor heater would help on migration