    Control scenario



    I came across a system the other day that looks as though a mistake was made in the control scenario. Water cooled R12 recip. compressor. 3 ton TXV, external equalized. Liquid line solenoid valve. Hot gas solenoid valve feeds hot gas regulator to side inlet of outlet of TXV. Temperature control is done by pressure switch on suction of compressor. When command to cool is issued ALL solenoids are energized. Now pressure
    switch has control of the compressor start/stop.
    Pressure switch set to maintain 5-8*C space temp.
    As space temp. drops suction pressure will drop, but hot gas kicks in and raises suction pressure
    so unit will never satisfy low pressure switch. There is a hand valve feeding the hot gas solenoid that if closed allows system to pull down and cycle on pressure switch. I think what happened here is that unit was controlled by temp.
    at one time and someone decided to use pressure type control but never took the hot gas into consideration. Current control scenario doesn't make sense. How can you have pressure control and hot gas bypass at the same time? I have some ideas
    floating around. One scenario that surfaced was that maybe they were regulating that hand valve to feed a little hot gas in to keep the evap. active and promote some oil return? Note that when the pressure switch satisfies the solenoids remain energized. Only thing that kills power to them and starter is computer command to stop cooling, also stops evap. blower. Soliciting
    thoughts, comments, concerns from fellow fridgeheads.
    Mike Hopkins



  2. #2
    Join Date
    Dec 2001
    Location
    Italy
    Posts
    19
    Rep Power
    0
    Hi Mike,
    there are two main lines I think you have to follow to solve such a trouble.

    1) Why is there this hot gas bypass? Is that system designed for a high pressure work? What kind of service the system does?

    2)Obviously the wiring is incorrect; when the temperature is reached, the liquid solenoid and even the hot gas solenoid must be de-energized, if the scenario has to be a pump down-like.

    Try investigate these paths.
    Have a nice day

  3. #3
    Join Date
    Apr 2002
    Location
    Nova Scotia Canada
    Posts
    16
    Rep Power
    0
    I believe you should put temp control in the system to cycle liquid and hot gas solenoid to pump down and turn off the compressor. The hot gas line must have been installed to false load the system perhaps the compressor was desiged a little big for the system. However keeping the soleniods open with the compressor off sounds a little risky to me causing flood back on start up.

  4. #4
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23
    Two statements need elucidation: "Hot gas solenoid valve feeds hot gas regulator to side inlet of outlet of TXV." What kind of regulator? Is it maintaining minimum evaporator pressure? What kind of system is this cooling or intended to cool?

    2nd: "Only thing that kills power to them and starter is computer command to stop cooling, also stops evap. blower." Does this computer monitor the controlled medium/space temperature or is it simply periodic start-up/shut-down?

    First thought is that pressure control is not intended to control temperature, just to shut compressor off after pump-down, but some tech has misunderstood system and set press control higher in an attempt to control space temp. Depends on answers to above.

    Rog

  5. #5
    Timsutton2's Avatar
    Timsutton2 Guest

    Re: Control scenario

    These systems should be sized close to the load of the box and load added within the box. The hot gas solenoid opens when the space temp is reached and raises the temp of box slightly and shuts back off. This allows for a flat line on box temp. and keeps these compressors operating. They don't cycle compressors except to defrost. This gives longer compressor life. You will see these types of boxes on scientific boxes. We have installed and serviced many.

  6. #6
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    764
    Rep Power
    25

    Re: Control scenario

    Quote Originally Posted by Timsutton2 View Post
    These systems should be sized close to the load of the box and load added within the box. The hot gas solenoid opens when the space temp is reached and raises the temp of box slightly and shuts back off. This allows for a flat line on box temp. and keeps these compressors operating. They don't cycle compressors except to defrost. This gives longer compressor life. You will see these types of boxes on scientific boxes. We have installed and serviced many.
    Bingo! Except something has to cycle the hot gas bypass on and off or the regulator must be set to keep evap temp at design - eg open and false load the comp on a lowering of evap pressure.
    Sounds like maybe the regulator is not doing what it should and allowing the suction pressure to fall lower thereby allowing the room temp to fall - hence somebody has set the LP to cycle and keep temp, a bit of a compromise on the original intention.
    What sort of regulator is it? Is it adjustable?

Similar Threads

  1. Replies: 21
    Last Post: 05-07-2008, 10:48 AM
  2. Short Cycling blues & low pressure control switch
    By mccoolair@yahoo in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 09-04-2006, 09:28 PM
  3. Heat pump temperature control
    By Vincent Yu in forum Fundamentals
    Replies: 8
    Last Post: 30-09-2005, 12:50 PM
  4. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 02:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •