    Daikin vrv control wiring



    (a) Approx 8 outdoor units.
    (b) Approx 98 indoor units.

    Would it be possible to daisy chain all indoor units e.g starting from top floor all the way down to the bottom floor and also link the outdoor units?
    There will be no central control used on the project. All units will be individually controlled.
    I have a feeling that I will have to daisy chain the vrv's individually, which will be unfortunate!

    regards
    Jase



  2. #2
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Smile Re: Daikin vrv control wiring

    Jase each systems indoor fan coils F1 & F2 wiring have to be kept seperate. Even when not using a Centralised controller i would still recommend connecting the F1 & F2 outdoor connections on your eight outdoors this will enable the sequential start. If you need any more help just let us know the model numbers of your units

  3. #3
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Daikin vrv control wiring

    Cheers for the advice puddleboy!

  4. #4
    pasausang's Avatar
    pasausang Guest

    Re: Daikin vrv control wiring

    Hello puddleboy3

    send to me type:PC9316


    Thanks & Regards

  5. #5
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Daikin vrv control wiring

    Hi Jase,
    There is impossible to daisy chain all indoor units, should be system by system seperately as puddleboy said.
    If not over capacities error, spec are 130% or 200% option for cooling only unit and 150% for heatpump.
    Daikin never locked and prompted as capactiy error unlike others.
    However please seperate.

Similar Threads

  1. Transmission wiring on Daikin VRV2
    By Markie in forum Air Conditioning
    Replies: 19
    Last Post: 25-09-2009, 06:24 PM
  2. Control scenario
    By Mike Hopkins in forum Technical Discussions
    Replies: 5
    Last Post: 14-09-2007, 11:25 AM
  3. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM
  4. Required Control Wiring 50dp-020-910 Carrier
    By altaf22m in forum Air Conditioning
    Replies: 2
    Last Post: 08-08-2005, 06:08 PM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •