    Daikin wall split



    Hi
    I have a Daikin cooling only wall split FTKS25EVMA, the indoor fan works and the unit accepts the commands from the controller, but the outdoor unit will not start even when pressing the pump down button. I have fault checked the indoor unit and nothing comes up, just get a long bleep on 00. Daikin are no help without a fault code. All the circuit boards have been swapped out but still nothing. Anyone had this before or have any suggestions.

    Thanks



  2. #2
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: Daikin wall split

    it may be something too simple.check the wiring or make a reset (power off for a couple of minutes).also ,check for the applied voltage.it should be within limits.

  3. #3
    Join Date
    Feb 2015
    Location
    India
    Posts
    43
    Rep Power
    0

    Re: Daikin wall split

    @martin102 could you check following:
    (1) Does the outdoor unit's cooling fan starts or not?
    (2) If outdoor unit's fan doesn't start then supply wires to the outdoor unit must have gotten disconnected
    I maintain, everything I have, myself.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin wall split

    check green led's on indoor and outdoor boards- should flash when communicating shoud be mains voltage on 1,2 2-3 should be a pulsing signal around 100v ac - if its inverter the outdoor fan starts up first- usually a dc motor so if that isnt happening maybe thats at issue

  5. #5
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Daikin wall split

    Indoor and outdoor green led's flash, the indoor continuously but the outdoor flashes 7 times then does a short flash.? I have checked and replaced interconnecting wiring, replaced all the pcb's inside and out, checked thermistors, and have now replaced the whole system :-)
    I now have the faulty system set up in my shed, because I would like to find out the cause of the fault.
    Indoor fan motor is new, haven't seen the outdoor fan start, checked the windings and all seem fine according to the Daikin training book, I have worked on Daikin's for years and never come across this problem. Daikin tech support is useless as they need a fault code, all I get is 00 which they say is normal.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin wall split

    When you had the 00 up did you then scroll through all of the fault codes using the temp up/down button?

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin wall split

    did the indoor pcb req a capacity set plug?

  8. #8
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: Daikin wall split

    Did you do a diode check on the outdoor fan motor? I have had the outdoor fan motors fail and the windings test ok but because the diode is faulty it draws the DC volts out of the PCB and in some cases damages the new pcb that you put in.

  9. #9
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: Daikin wall split

    can be more specific about that kind of troubleshooting?

  10. #10
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Daikin wall split

    Yeah, went through all the codes

  11. #11
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Daikin wall split

    Outdoor unit model RKS25EVMA

  12. #12
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Daikin wall split

    Quote Originally Posted by install monkey View Post
    did the indoor pcb req a capacity set plug?
    Daikin don't supply one, it is just a straight swap out

  13. #13
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Daikin wall split

    Quote Originally Posted by Keza View Post
    Did you do a diode check on the outdoor fan motor? I have had the outdoor fan motors fail and the windings test ok but because the diode is faulty it draws the DC volts out of the PCB and in some cases damages the new pcb that you put in.
    Checked the motor against the Daikin training book, all fine