    Compressor going out on thermal cut out



    Hi,

    I look after a chiller that is comprised of two circuits, each with one hitachi screw compressor.

    One of the circuits will run for hours and hours, but eventually trip out and 'comp thermal trip' is displayed on the digital interface. I've proved that it's definitely the klixon breaking to bring this error up, however I haven't witnessed it cutting out with my own eyes, I'll leave it, go and do something else, check it now and then, and sometimes it can take up to a whole day to cutout. It seems to run as well as the other circuit. Here are some circuit readings from both.

    Condenser coils are clean.

    Compressor 1 (no problems)

    Ref - R407C
    Evap pressure - 4.5 BarG
    Evap temp - 5°C (approx)
    Suction pipe temp - 12°C
    Superheat - 7K

    Entering water temp - (between 12-15°C fluctuating)
    Leaving water temp - 6°C (this is setpoint - and therefore operation stops when this is satisfied).

    Condensing pressure - 14.5 BarG
    Cond. temp - 40°C
    Discharge pipe temp - 60°
    Liquid line pipe temp - 30°C
    Subcooling - 30K
    De-superheating - 30K

    Compressor running amps - approx 20-21A

    1kV winding resistance check

    U to V - over 1000 Giga ohms
    V to W - over 1000 Giga ohms
    U to W - over 1000 Giga ohms

    Earth insulation check

    U to earth - 800 + mega ohms
    V to earth - 800 + mega ohms
    W to earth - 800 + mega ohms

    Compressor 2 (thermal trip error)

    Ref - R407C
    Evap pressure - 4.5 BarG
    Evap temp - 5°C (approx)
    Suction pipe temp - 12°C
    Superheat - 7K

    Entering water temp - (between 12-15°C fluctuating)
    Leaving water temp - 6°C (this is setpoint - and therefore operation stops when this is satisfied).

    Condensing pressure - 14.5 BarG
    Cond. temp - 40°C
    Discharge pipe temp - 60°
    Liquid line pipe temp - 30°C
    Subcooling - 30K
    De-superheating - 30K

    Compressor running amps - approx 24-29A

    1kV to earth resistance check

    U to V - not going over 300 mega ohms
    V to W - over 1000 MEGA ohms
    U to W - over 1000 MEGA ohms

    U to earth - around 280 mega ohms
    V to earth - 800 + mega ohms
    W to earth - around 500 mega ohms


    Operation wise it seems ok, therefore I'm thinking it's likely I've got an issue with the windings on compressor two.

    Thoughts??

    Any checks you suggest I should carry out?

    Thank you
    Last edited by halfcan; 10-04-2017 at 08:03 AM.



  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: Compressor going out on thermal cut out


  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Compressor going out on thermal cut out

    Quote Originally Posted by halfcan View Post
    Hi,

    I look after a chiller that is comprised of two circuits, each with one hitachi screw compressor.

    One of the circuits will run for hours and hours, but eventually trip out and 'comp thermal trip' is displayed on the digital interface. I've proved that it's definitely the klixon breaking to bring this error up, however I haven't witnessed it cutting out with my own eyes, I'll leave it, go and do something else, check it now and then, and sometimes it can take up to a whole day to cutout. It seems to run as well as the other circuit. Here are some circuit readings from both.

    Condenser coils are clean.

    Compressor 1 (no problems)

    Ref - R407C
    Evap pressure - 4.5 BarG
    Evap temp - 5°C (approx)
    Suction pipe temp - 12°C
    Superheat - 7K

    Entering water temp - (between 12-15°C fluctuating)
    Leaving water temp - 6°C (this is setpoint - and therefore operation stops when this is satisfied).

    Condensing pressure - 14.5 BarG
    Cond. temp - 40°C
    Discharge pipe temp - 60°
    Liquid line pipe temp - 30°C
    Subcooling - 30K
    De-superheating - 30K

    Compressor running amps - approx 20-21A

    1kV winding resistance check

    U to V - over 1000 Giga ohms
    V to W - over 1000 Giga ohms
    U to W - over 1000 Giga ohms

    Earth insulation check

    U to earth - 800 + mega ohms
    V to earth - 800 + mega ohms
    W to earth - 800 + mega ohms

    Compressor 2 (thermal trip error)

    Ref - R407C
    Evap pressure - 4.5 BarG
    Evap temp - 5°C (approx)
    Suction pipe temp - 12°C
    Superheat - 7K

    Entering water temp - (between 12-15°C fluctuating)
    Leaving water temp - 6°C (this is setpoint - and therefore operation stops when this is satisfied).

    Condensing pressure - 14.5 BarG
    Cond. temp - 40°C
    Discharge pipe temp - 60°
    Liquid line pipe temp - 30°C
    Subcooling - 30K
    De-superheating - 30K

    Compressor running amps - approx 24-29A

    1kV to earth resistance check

    U to V - not going over 300 mega ohms
    V to W - over 1000 MEGA ohms
    U to W - over 1000 MEGA ohms

    U to earth - around 280 mega ohms
    V to earth - 800 + mega ohms
    W to earth - around 500 mega ohms


    Operation wise it seems ok, therefore I'm thinking it's likely I've got an issue with the windings on compressor two.

    Thoughts??

    Any checks you suggest I should carry out?

    Thank you
    In such case, there is a problem inside the windings o that compressor.
    I guess it is hermetic one. Only 3 wires coming out.
    Just replace it and save time and future problems.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Compressor going out on thermal cut out

    hitatchi screw chemi- prob 6 wires coming out as it will be part wind or star delta
    but as your windings aren't balanced and 1 winding to earth is much lower than the others, also increased running current- maybe try and limit capacity to 40% to prolong having to change it(reduce the running current to prevent it going out on klixon)

  5. #5
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Compressor going out on thermal cut out

    Hi halfcan
    Try replacing the liquid line filter driers and oil charge before doin anything drastic and leave it running
    for a few days to see if the windings resistance improves in case the system has any moisture or acid inside which the drier with any luck with may come to your rescue.
    Use a quality drier like a Danfoss DM or Sporlan HH

  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Compressor going out on thermal cut out

    Hi
    Do what Mr.gelnn told
    And it better change filter with anti acid core
    Also check PH of oil
    And check resistance of oil by megger
    Last edited by mbc; 11-04-2017 at 06:43 PM.

  7. #7
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: Compressor going out on thermal cut out

    Quote Originally Posted by mbc View Post
    Hi
    Do what Mr.gelnn told
    And it better change filter with anti acid core
    Also check PH of oil
    And check resistance of oil by megger
    oil resistance by megger??
    can you explain me that procedure?