    Refrigerant Critical Temperature



    hey guys

    If you heat a gas above its critical temp the refrigerant will not condense no matter what the pressure is, but if you reduced the temperature back down below critical temp, will it the be able to change state again?

    why i ask is that back at TAFE me teacher told me the gas would be "burnt" and result in the gas never being able to change state again and would need to be replaced.
    i work with another technician who disagrees. what are your thoughts?



  2. #2
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Refrigerant Critical Temperature

    I dont think thats necessarily true about going over the critical temperature , but i can tell you that if 404 is run at high pressure and temps (blocked condenser) for long period of time it loses its efficiency and ability to evaporate at low temperatures, this is always accompanied by a burnt smell from the gas in the system.

  3. #3
    Join Date
    Mar 2010
    Location
    Lisbon
    Posts
    55
    Rep Power
    16

    Re: Refrigerant Critical Temperature

    Hi,
    The critical point is above, both a certain temperature and pressure. At low pressure when you cool the gas obviously it will condensate again.
    Above critical point you need to reduce pressure in order to be able again to condensate and evaporate the fluid.
    If you take a look at the PH diagram (Mollier chart) this relations become more obvious.
    If you heat it too much maybe you can transform the substance and if it degradates maybe you can not achieve again the original state, that I dont know.
    Regards,
    CDuqueDiag P-H.PNG

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Refrigerant Critical Temperature

    .

    Hello

    I think the issue is with man made refrigerants (synthased) HFC based refrigerants.

    Natural refrigerants like R744 (C02) tend not to burn out.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Refrigerant Critical Temperature

    Critical temperature is where conventional refrigerants degrade.

    One instance was an R134a vehicle air-conditioner that had a bypassed HP/LP and a seriously inefficient condenser. ( Blocked with grass seed and Insects.) Cleared that drama but the A/C wouldn't perform.

    Some of the refrigerant condensed. Liquid pressure and temperature remained high.
    Pulled the R134a, replaced the drier, and vacuum. Fresh charge of refrigerant. Customer is happy with the outcome.
    Compressor oil contamination? I Have No Idea.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Refrigerant Critical Temperature

    Quote Originally Posted by cduque View Post
    Hi,
    The critical point is above, both a certain temperature and pressure. At low pressure when you cool the gas obviously it will condensate again.
    Above critical point you need to reduce pressure in order to be able again to condensate and evaporate the fluid.
    If you take a look at the PH diagram (Mollier chart) this relations become more obvious.
    If you heat it too much maybe you can transform the substance and if it degradates maybe you can not achieve again the original state, that I dont know.
    Regards,
    CDuqueDiag P-H.PNG
    You are on the right Path though Charts can't predict molecular transformation.
    Last edited by mikeref; 11-04-2017 at 09:20 AM. Reason: Thought about going into detail.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    Mar 2010
    Location
    Lisbon
    Posts
    55
    Rep Power
    16

    Re: Refrigerant Critical Temperature

    There in no critical temperature but a critical point and it is established both in temperature and pressure.
    So it is not possible to heat the gas over the critical point if the pressure is not high enough.
    Also there is not any connection between one fluid "degradation" or "burn out" point and it's critical point.
    Several fluids, for instance R744 (CO2), doesn't burn or degradate much over it's critical point.

  8. #8
    Join Date
    Nov 2014
    Location
    Australia
    Age
    30
    Posts
    16
    Rep Power
    0

    Re: Refrigerant Critical Temperature

    cool guys, thanks for the input.

    the example with R744 is perfect. i have been referencing "critical point" with "refrigerant degrading", which has been incorrect. although with R404A these two points seem to be close.

    it would be very advantageous to have a chart with some temperatures at which some of these refrigerants begin to de-grade

    cheers everyone

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Refrigerant Critical Temperature

    It happens a lot with 404 for unknown reason to me.

    I have came across quite a few systems that had a full charge and all seems to be ok but no cooling.
    replacing the charge made it work fine again, so to my humble opinion, your teacher is right.

  10. #10
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Refrigerant Critical Temperature

    Many years ago an experienced engineer referred to the refrigerant becoming 'tired' and would therefore require replacing. Whether this was convenient bulls*** for the customer or not, I am not sure. But maybe there was a minor element of truth in what he was saying.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  11. #11
    Join Date
    Nov 2014
    Location
    Australia
    Age
    30
    Posts
    16
    Rep Power
    0

    Re: Refrigerant Critical Temperature

    Quote Originally Posted by hyperion View Post
    Many years ago an experienced engineer referred to the refrigerant becoming 'tired' and would therefore require replacing. Whether this was convenient bulls*** for the customer or not, I am not sure. But maybe there was a minor element of truth in what he was saying.
    Refrigerant being "tired", I call BS on that one.

    it seems to always occur due to high head issues, the gas always stinks too.

  12. #12
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: Refrigerant Critical Temperature

    HmmKay,

    So - I'm thinking you are dealing with Two different matters (critical point and then "decomposition")

    Let's talk about critical point - let's talk about something called R134a, some people may have heard of it. Critical point is 101 C. Let me ask you a question "in your educated opinion, could we heat refrigerant r134a to 102 Celciuls, then cool it down & continue to use it per usual"

    Well yes, I think so. I could put tap water in a pressure cooker, heat that to 102 Celsius then dunk a tea bag. Just real hot tea - wait 'till it cools down same same.

    Now, second matter - decomposition. Let's remember that refrigerants are made from elements from the periodic table. Now let's imagine what might happen should All the tetras and all the flouros and all the ethanes were "separate" into their respective elements.... Would that make for some "tired" frigo. Pretty sure if my body decided to separate into its periodic elements I'd be a bit tired..

    Now could refrigerant actually separate?

    This a a question that many like to sweep under the carpet..

    I'm sure you can make your own judgement.... (hint, think about what might happen during winding burnout or extended operation at elevated temperatures)

    Ps, I know what happens to a piece of wood when it operates at elevated temperatures (it cannot retain its original form for very long, before turning into smoke...)

  13. #13
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Refrigerant Critical Temperature

    I like your thinking HVACR.
    If refrigerant doesn't split! Then how come some have to be charged in their Liquid state only.
    In fairness to all concerned!
    If as we know some refrigerants will split into their constituent gases under certain conditions. Then surely they
    could leech out of a system at variable rates.
    Resulting in a refrigerant which is no longer the same as original!

    Either way anything used at the extremes of their operating range, will suffer.
    A very interesting post all the same.
    No-one has yet mentioned that the refrigerants at the elevated temps, will likely contain oil in them as well.
    Unless it's a Turbocore.
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  14. #14
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Refrigerant Critical Temperature

    Quote Originally Posted by thebrockenshire View Post
    Refrigerant being "tired", I call BS on that one.

    it seems to always occur due to high head issues, the gas always stinks too.
    5 posts and you are already accusing other valued posters of "Bull ****".
    A bit harsh for one so new to the forum don't you think?
    whether you call something Tired or degraded or split or stinky!
    It's only a term to describe something not correct.
    So why the accusation of BS?
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  15. #15
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Refrigerant Critical Temperature


  16. #16
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Refrigerant Critical Temperature

    Yes I agree although I have health issues etc,resorting to words that are best kept to oneself as grizzly says is out of order! I visit many social media sites but bad language is a no no,it does not respect intelligence and if you have to resort to it then think before sharing/ commenting but hey it's only my opinion!

  17. #17
    Join Date
    Nov 2014
    Location
    Australia
    Age
    30
    Posts
    16
    Rep Power
    0

    Re: Refrigerant Critical Temperature

    Quote Originally Posted by Grizzly View Post
    5 posts and you are already accusing other valued posters of "Bull ****".
    A bit harsh for one so new to the forum don't you think?
    whether you call something Tired or degraded or split or stinky!
    It's only a term to describe something not correct.
    So why the accusation of BS?
    Grizzly
    My apologises, my comment being a bit heavy handed.
    my interpretation being the refrigerant becoming "tired" due to general use. which I cannot relate to.

  18. #18
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Refrigerant Critical Temperature

    Ranger1,
    Interesting article.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.