    Dear Friends,

    When we pump down a cycle, after a while pressure of suction increases, Would it be possible to let me know :

    Increasing suction pressure is as result of leakage on discharge valve or it is as result of leakage on liquid line solenoid valve ?
    It means, Discharge valve can not 100% close the route or liquid line solenoid valve can not 100% close liquid line ?

    Which one is true ?

    Sincerely yours.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Question about pump down

    Most likely neither.

    If we assume that you mean that the pressure rises after the compressor stopped and that it doesn't reach saturated pressure levels.
    Your refrigerant cycle does not only carry refrigerant, there will also be oil with the refrigerant. This oil will bind with refrigerant and the amount of refrigerant mixed with the oil depends on the pressure, when we lower the pressure the refrigerant in the oil will start to boil off (or be released) and this will slowly increase the pressure.


  3. #3
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16

    Re: Question about pump down

    The pressure will also increase due to temperature change upwards.

  4. #4
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Question about pump down

    it can depend on a few things.

    Length of the suction line, design of the suction line, evaporator temperature.

    Let's say there is a room thermostat controlling the solenoid valve, when the temperature in the room is reached, it closes the solenoid, when the temperature in the room is reached, it means that all the products in the room has reached, or are very close to the same temperature as the evaporator temperature.

    So there is not much heat load on the evaporator, but there may still be liquid refrigerant left in the evaporator after the first pump down, and the tiny heat load will in time cause the refrigerant to evaporate and increase the pressure, causing the LP-switch to cut in and start the compressor.

    Or it could be a long suction line, with a pressure drop, or as The Viking said, oil residue containing refrigerant in the evaporator/suction pipe that evaporates and causes a increase in pressure.

    in both cases, the compressor will start and stop a few times before it finally has emptied the system and there is not enough refrigerant left to evaporate.

    To diagnose a leaking solenoid valve, check if there is constant ice/freezing on the pipe between the solenoid and the thermostatic expansion valve when the compressor pumps down.

    On the systems we have delivered, we like to put a 5 minute timer relay in the pump down function, so the compressor doesn't cut in and out too much during a pump down cycle, to protect the compressor from running for a few seconds and not build up oil pressure, and to give the start contactor a longer life.

    Hope this Helps
    -Cheers-

    Tycho

  5. #5
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Re: Question about pump down

    Thanks friends for your replies.

    Sincerely yours.

  6. #6
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16

    Re: Question about pump down

    Animated description of a non-recycling pump down circuit......

    http://www.refrigerationbasics.com/RBIII/controls5.htm

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Question about pump down

    Quote Originally Posted by FaultCode View Post
    Animated description of a non-recycling pump down circuit......

    http://www.refrigerationbasics.com/RBIII/controls5.htm