    Lightbulb Petra water chiller



    hi friends i am facing a unusual problem with PETRA make water chiller model no-RWC 210, water accumulating in compressor, there are two scroll compressors and heat exchanges ..this is the second time this issue happened, kindly please help me to rectify the root cause.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Petra water chiller

    Basically it sounds as if one or both heat exchangers are leaking allowing water into the refrigerant circuit.
    You need to prove the gas tightness of your refrigeration system.
    Good Luck
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  3. #3
    Join Date
    Aug 2016
    Location
    India
    Age
    37
    Posts
    8
    Rep Power
    0

    Re: Petra water chiller

    sir i have installed two new compressors of Copeland and two new heat exchanges of danfoss make, than too water accumulated inside the compressors.

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Petra water chiller

    When you recommissioned the chiller after you replaced the compressors and evaporators, did you check and verify the function of all the safety devices? Glycol level of the chilled media, if running close to freezing?

    The most likely scenario is that the first evaporator froze up and this caused it to leak, a new evaporator was then fitted but if the cause of the original freeze-up wasn't fixed the new evaporator suffered the same fate as the first one.