Thread: Sabroe 283 oil lose
01-04-2017, 05:49 PM #1
Sabroe 283 oil lose
Hello guys
I am new here and I have one problem in sabroe283 new system oil loss within 1week operation we check oil return resievor and filters oil sepreator its normal and suc, disch pressure also can you anyone suggest me what is possibility
05-04-2017, 04:01 PM #2
- Sep 2009
- Iran
- 66
- 672
- 1
- 19
Re: Sabroe 283 oil lose
HI
It is small reg valve in the second oil separator and after that is a sight glass and then again small reg valve
Both of them should be open a little to return oil to system again from 2nd one
If you need more information please let me know
Also
did you choose right oil
Your suction filter should be clean and did you remove cotton from inside of your suction filterLast edited by mbc; 05-04-2017 at 04:05 PM.
06-04-2017, 01:31 PM #3
New Compressor Unit? Check the strainer on the oil return control valve. But if it is a new machine perhaps you should call the manufacturer to commission machine. This is not the job for someone who does not know! Safety first!!