29-03-2017, 10:29 PM #1
Noisy expansion valve
Evening all,
A site we look after has 3 Eaton Williams IPAC close control type units. One of them when switching off has an extrnally equalised TEV which makes a whining/hammering noise. From the sight glass it looks like it passes refrigerant for a few minutes after the compressor stops. Is this something I should be concerned about, will liquid pass into the evaporator and compressor when next starting. It seems to run okay with superheat okay but others say it has frozen up in the summer but I have not witnessed this.
Help very much appreciated.
-
30-03-2017, 04:42 AM #2
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Noisy expansion valve
hi
orifice of your TEV is not sealing good and passing liquid from equalized line
change it and then adjust it again
Before that close TEV about half circle see what happenLast edited by mbc; 30-03-2017 at 04:48 AM.
-
30-03-2017, 06:11 AM #3
Re: Noisy expansion valve
Thanks mbc,
I will give it a go, what would closing down by half do, won't this change the superheat?
-
30-03-2017, 09:12 AM #4
Re: Noisy expansion valve
Most Close Control systems have a liquid line solenoid valve. If the system has one you need to check the valve is closing when the compressor stops.
-
30-03-2017, 04:01 PM #5
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Noisy expansion valve
Hi
It changes the super heat but this much is not too important