    Noisy expansion valve



    Evening all,

    A site we look after has 3 Eaton Williams IPAC close control type units. One of them when switching off has an extrnally equalised TEV which makes a whining/hammering noise. From the sight glass it looks like it passes refrigerant for a few minutes after the compressor stops. Is this something I should be concerned about, will liquid pass into the evaporator and compressor when next starting. It seems to run okay with superheat okay but others say it has frozen up in the summer but I have not witnessed this.

    Help very much appreciated.



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Noisy expansion valve

    hi
    orifice of your TEV is not sealing good and passing liquid from equalized line
    change it and then adjust it again

    Before that close TEV about half circle see what happen
    Last edited by mbc; 30-03-2017 at 04:48 AM.

  3. #3
    Join Date
    May 2008
    Location
    UK
    Posts
    170
    Rep Power
    16

    Re: Noisy expansion valve

    Thanks mbc,

    I will give it a go, what would closing down by half do, won't this change the superheat?

  4. #4
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Noisy expansion valve

    Most Close Control systems have a liquid line solenoid valve. If the system has one you need to check the valve is closing when the compressor stops.

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Noisy expansion valve

    Hi
    It changes the super heat but this much is not too important