    the best way to recharge a VRV/VRF



    Whats the best way to recharge a VRV/VRF system? In the suction side? in liquid form or vapour form? what about when you have dumped charge as much as possible and you have to get more in when the unit is running, whats the best way?
    remeber for all us newbies out there its only easy if you know it!!



  2. #2
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: the best way to recharge a VRV/VRF

    Hi,

    Well, if yoy are going to use a full bottle (Dumpys or reclaim) you can fill vapour as you will empty the bottle so getting everything out, If the unit has a test mode (Daikin for instance) then use this as this will run the unit at full capacity helping to get the gas in.

    Usuall rule is that you shouldn't liquid charge without the correct adapter in line (Anyone actually got one ?) but otherwise SLOWLY fill with liquid. You will soon hear the compressor change sound if you are doing it too quick.

    Have you a specific unit in mind so we can go into more detail or is this a theory question

    Regards

    Fatboy

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: the best way to recharge a VRV/VRF

    im working on a mistubishi heavy duty tomorrow which i will be recovering supposedly 21kg of r407c and then recharging with totally new refigerant if this helps

  4. #4
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: the best way to recharge a VRV/VRF

    The charge needs to be weighed in correctly, and as it's R407C liquid charged. My preferred method is to charge as much as possible with it under vacuum. When the scales stop moving, then get it running and charge in liquid form, which will have to be into the suction line. Throttle back the flow of refrigerant through the charging line sufficiently that it will allow the liquid to vaporise before it's compressed. I think that these machines use scroll compressors, which are somewhat more tolerant than reciprocating models as the scrolls tend to lift apart, but you still need to exercise caution. If you're in cooling mode the suction pipe should be cold to touch, but the only correct way is to weigh in the charge. I remember a similar thread to this some time ago relating to Daikin VRV's.
    Best of Luck
    James
    a problem shared is a problem halved

  5. #5
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: the best way to recharge a VRV/VRF

    Quote Originally Posted by marc5180
    im working on a mistubishi heavy duty tomorrow which i will be recovering supposedly 21kg of r407c and then recharging with totally new refigerant if this helps
    You MUST liquid charge R407C
    a problem shared is a problem halved

  6. #6
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: the best way to recharge a VRV/VRF

    Hi Guys,

    Yes i know all 400 gasses have to be charges liquid but has anyone actually done any research into what happens if you vapour charge.

    No i know that if you leave a bottle standing still the contens COULD !!! seperate and therefore not give the correct proportions when you charge but how often do you charge from a bottle thats stood still for a few weeks.

    Personally, Mine get shook about it the back of my van like they are on the roller coaster at blackpool. Then they get taken out of the van and are shook about while carried to the unit.


    My Question is this "How long would it take for a bottle to be completly stood still for the gas to seperate and therefore cause a problem when used"

    Any ideas

    Fatboy

  7. #7
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: the best way to recharge a VRV/VRF

    Refrigerant blends are made of gasses that have different boiling points
    It's not that they separate like oil and water. It's when you charge with vapor one gas boils off at a different temperature than the other so leaves the bottle before the one with higher boiling point.

  8. #8
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: the best way to recharge a VRV/VRF

    R407C is made of R32, R125 and R134a. R32 is the most volatile and so when you are charging, the pressure in the bottle drops and causes the R32 to vaporise first, causing the wrong proportions to be charged. Because of the different characteristics the temperatures and pressures are affected along with operating characteristics
    a problem shared is a problem halved

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: the best way to recharge a VRV/VRF

    Does anyone still use the old charging rigs? If you measured the charge into the rig then you could safely charge 400 series gases as vapour

  10. #10
    Join Date
    May 2006
    Location
    france
    Posts
    3
    Rep Power
    0

    Re: the best way to recharge a VRV/VRF

    the fan coil connected to a central vrv system ( R407C) has to condensate water during the cooling phase. Such water are collected and drained to pump. However it is found that few droplets are not following the circuit described here above and seems to be ejected with air as a droplets

    ANY BODY HAS BEEN ATTENDED to such trouble shooting?

  11. #11
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: the best way to recharge a VRV/VRF

    For some reason your face velocity is too high. Any chance you are missing a filter, or have the incorrect fan assembly? These units are designed to avoid entraining moisture back into the air. Maybe something is blocking a portion of the coil, causing a high velocity through the free area.

  12. #12
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: the best way to recharge a VRV/VRF

    yer making a big job of this chaps ! ever thought of sticking the bottle on the scales,connecting to the liquid line as you should with blends,connect your recovery machine to the bottle and pump the correct charge in, thats how i do the big chillers to get round the pressure equilisation.

  13. #13
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: the best way to recharge a VRV/VRF

    We had just installed an VRV and found the service port passing.We could not pressure test the system as the nitrogen would push passed the service valve making readings useless.Also risking nitogen in the outdoor unit.Also a vac would never pull down until the unit had lost it's charge.We had to reclaim the 410a from the hole system ,pressure test and vac ,after which we put the correct charge in as liquid on scales.The charge was written on the side of the unit 4.8Kg. £220 of gas and a days work chasing around for equiptment.We were the sub contactors(hope the company who purchased the unit can claim that back).Else they will not be asking us back again on price.The risk we will have to take on doing a good job.

  14. #14
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: the best way to recharge a VRV/VRF

    The charge was written on the side of the unit 4.8Kg.
    This seems awfully low for a VRV charge. Was it the whole charge or just the additional charge?

  15. #15
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: the best way to recharge a VRV/VRF

    4.8Kg this was all we put in. I assume it was the whole charge as this was on the system plate. We also checked with the supplier. He came up with the same number. When we recovered the gas it was about 4. Something Kg. could not be sure as the scales kept switching off. When we charged it the 410a slowed at this point like the system was balanced with the bottle pressure. Not an exact science but it seems to be about right in most cases I found. AirStage J-series

  16. #16
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: the best way to recharge a VRV/VRF

    Are you sure it was a vrv/vrf/ sounds more like a multi unit to me. Iv never come across a Vrv that only holds 4.8kg

  17. #17
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: the best way to recharge a VRV/VRF

    Quote Originally Posted by old gas bottle View Post
    yer making a big job of this chaps ! ever thought of sticking the bottle on the scales,connecting to the liquid line as you should with blends,connect your recovery machine to the bottle and pump the correct charge in, thats how i do the big chillers to get round the pressure equilisation.
    hello mate,
    could you please go into a bit more detail please on this method i.e do you have gauges inline fully open and recovery unit set to liquid cheers mate

  18. #18
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    243
    Rep Power
    18

    Re: the best way to recharge a VRV/VRF

    daikin seam to be having a few probs lately with service ports passing. When pressure testing you think you got a leak then find that its the port passing and got to reclaim the gas, not good

    adam

  19. #19
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: the best way to recharge a VRV/VRF

    Here's my question and a possible answer!

    When the valves leak, did you braze the couplings while they where on the valves?


    If so there's the answer as to why they leak! The heat damages the seals in the valves!

  20. #20
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: the best way to recharge a VRV/VRF

    Quote Originally Posted by marc5180 View Post
    Are you sure it was a vrv/vrf/ sounds more like a multi unit to me. Iv never come across a Vrv that only holds 4.8kg
    These J series where only 15kW units and I suppose with R410a you can do quite a bit of work.
    Brian - Newton Abbot, Devon, UK