    How to recover from a VRV properly



    whats the best method to recover refrigerant from a 3 pipe vrv/vrf system? is it the push pull method if so wats the best way to do it?



  2. #2
    Join Date
    Dec 2005
    Location
    Manchester England
    Posts
    19
    Rep Power
    0

    Re: How to recover from a VRV properly

    Does the compressor run? If so run it in cooling mode and attach your bottle to the liquid line.Use your scales to check how much comes out. When you can't get anymore out, switch off and use your reclaim machine on all sides.

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: How to recover from a VRV properly

    I would be careful about recovery with the compressor running, because of lubrication to the compressor, eventually the motor will overheat, but in any event as it's a VRV the LP trip should shut off.
    a problem shared is a problem halved

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: How to recover from a VRV properly

    The correct method is to put the machine into recovery mode using the dip switches on the outdoor pcb. This sets all the indoor tev's to the fully open position then you can recover as normal.

    Read the instructions on the inside of the outdoor cover panel.

Similar Threads

  1. upside down fridge/freezer not cooling properly
    By Barney01 in forum Domestic
    Replies: 5
    Last Post: 07-10-2005, 08:20 AM
  2. is my fridge working properly?
    By vincec in forum Trouble Shooting
    Replies: 1
    Last Post: 15-01-2002, 09:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •