Results 1 to 16 of 16
    Feb 2016
    Uk
    48
    48
    Qualitair icing tev
    R410a cellar cooler
    10.7 degrees c superheat
    17 degrees c subcooling
    6 bar low side pressure
    24 bar high side pressure
    And the tev looks like this.
    I think it's not operating properly
    Any thoughts
    Many thanks in advance
    5,668
    Re: Qualitair icing tev
    Either low ambient with no head pressure control or sog
    cellar cooling is normally around 10 -13 C so evaporating around 4 - 6C...no chance of frost that those temps
    17K subcooling is excessive.
    try blocking the condenser and see what happens
    3,856
    High(ish) suction superheat and high liquid line subcooling point to underfeeding TEV, though also check air flow through evaporator coil/ coil cleanliness etc. Would expect lower superheat if the air flow was poor.
    I'd probably try warming the valve and phial to with some water to see if things improve even if only temporary. Could be partial loss of charge from the phial and bellows, or moisture/wax or dirty blocking the seat in the valve.
    Feb 2007
    2,473
    How far back does the frost go on your liquid line, before the TEV?
    Aug 2014
    75
    508
    Is this an internally qualified expansion valve? , it looks like a Danfoss TUB type .Have you any better pictures showing the valve evaporator and valve bulb positioning and if it's an internally equalised version ?.
    Feb 2016
    Uk
    48
    48
    Quote Originally Posted by Glenn Moore View Post
    Yes it is danfoss and does not have an equalising line just one in and one out
    And a bulb for the super heat
    Feb 2016
    Uk
    48
    48
    There is no frosting on the liquid line and I have high subcooling all up to the valve
    Jul 2006
    865
    Not my specialty, however I see the frost lead up to the TXV.
    Looks like a restriction in the liquid line. Solonoid valve or drier.
    Aug 2014
    75
    508
    It is unusual to fit an internally equalised valve to an evaporator that has a distributor fitted . The distributor and leads will have a large pressure drop and the expansion valve will not be able to offset this pd and will run with a too high superheat. Even trying to adjust the tee will not help unless you fit a externally equalised valve to remove the pd from the distributor.
    Fit a access valve to the expansion line to see what the pressure is there and then measure the suction pressure as well deduct one from the other to see what pd you have. More than a couple of psi difference change the valve to externally equalised
    Feb 2016
    Uk
    48
    48
    Thanks Glenn
    Think you are right all the other qualitair coolers I look after have an external equalising line on the tev.
    This unit is only a year old and probably one of the last ones out of the factory as qualitair have gone bust heaven knows why this one has a different valve on it.
    Anyway we have to honour our warranty and sort this out as we fitted although we bought it from dean and woods so see what they have to say first but as you say looking like a new valve.
    Many thanks again.
    Aug 2014
    75
    508
    I'm sure it will solve your problem,
    Best regards Glenn
    Jul 2006
    865
    My apologies and I feel like an idiot. When I looked at the picture I thought the liquid in was coming in from the lower part of the valve. I blew it up and saw my mistake.
    Am glad no one listened to me!
    Feb 2009
    telford
    2,090
    33
    Change the valve for one with an equaliser New filter drier,but the mystery remains it worked at some point? Ah well the fridge job does have a habit of biting back sometimes guess that's why we love it varied thermodynamics!
    Feb 2016
    Uk
    48
    48
    Quote Originally Posted by cadwaladr View Post
    I don't think it ever worked you can see where the customer has chipped away the ice as all the fins are bent or missing.
    Think we are going to replace the coil as well.
    Aug 2014
    75
    508
    Just for the record
    An internally equalised valve should only be used on small single circuit type of evaporators or evaporators with only 2-3psi pressure drop between the expansion valve and the evaporator outlet.
    Multi circuit evaporators that have distributors fitted must always use an externally equalised valve
    to overcome the pressure drop from the distributor head plus the distributor leads , this can be anything between 14 - 30 psi "or more in some cases" this will cause a massive loss of duty and high superheats etc with the wrong type of valve fitted
    4,707
    Thanks for the valued input Glenn.
    Sometimes we all forget the basics.
    The sign of a true Engineer is being able to admit when you get it wrong.
    Just like HN3LVR. (Who knew but misread a photograph.)
    Our industry is so big and diverse, you cannot get it right all the time.
    Which is why this forum is so good for all of us!
