Results 1 to 8 of 8
Thread: urgent
    Mar 2006
    Greece
    34
    Question urgent
    I have a Rack with 2 Bitzer compressors, 2 stage Model S6F30. The tunnels are -35 celcius. I replaced one of the compressors because the second stage valves (discharge valves) were broken. I noticed that the rear part of the new compressor, after the second stage suction, freezes. I closed the TXV of the sub-cooling one notch. The problem was solved, but after 2 hours of working properly, the same problem appeared. I closed the valve one more turn and the problem again fixed temporarily for about 2 hours. After the second time, I closed the TXV completely. The freezing problem disappeared again. I am now waiting to see the results in the morning. Superheat is 20 degrees celcius.
    I would appreciate any feedback. It is 10:00 pm and I will be going on site again in the morning. Thanks. Dimitri.
    Sep 2006
    Manila
    12
    Re: urgent
    Your valve doesn't feed enough. You should check the following:
    Shortage of refrigerant
    High Superheat
    Flash gas in line
    Faulty or dirty expansion valve
    Incorrect size of TXV
    Incorrect location of bulb
    Aug 2005
    5,302
    Re: urgent
    Dimitri,
    If the evaporating temperature is -35C and you have 20 degrees of superheat, the actual return gas temperature to the compressor is still -15C (5F). At that temperature the suction gas is still below the freezing temperature of water.
    Frost on a compressor housing does not mean liquid is present in the suction gas!
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: urgent
    I was in the process of answering, but Iceman was faster.
    With any setup, the suction of that compressor will be frozen. I don't see how it should not freeze, unless superheating will be more than 35°K, which is not a good idea.
    Let it freeze and rest in peace.
    Mar 2005
    58
    110
    Re: urgent
    As I understand it the freezing does not occure on the the suction side of the compressor, but on the intermediate stage.
    What is the pressure you have in the crank case ( = intermediate pressure) ?
    What is the superheat at the 'rear part of the compressor' (= second stage inlet) ?
    Oct 2004
    Scotland
    1,454
    21
    Re: urgent
    @NoNickName, this thread has been up for 4 months now...lol
    A snail walking around the world would be faster.
    Hehehe
    Chillin
    and go get a cuppa
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: urgent
    We gave you a chance of answering, chillingout, but in the last 4 months either you were too busy, or didn't care.
    The Saint brought the thread up and Iceman and myself didn't have a look at the posting date. It may help somebody else.
    Oct 2006
    Canada
    7
    Re: urgent
    Hey your valve is pouched, or your buld is in the wrong spot. What's your sub cooling at ? When's the last time you did a full PM ? What concerns me is that you have that TXV at full close (that's not good good)
  1. Urgent G Fault Codes Needed
    By botrous in forum Trouble Shooting
    Last Post: 08-08-2005, 08:13 PM
  2. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Last Post: 20-01-2004, 03:12 PM
  3. Urgent!!! S.O.S. - nozzle size
    By herefishy in forum Fundamentals
    Last Post: 25-05-2002, 10:29 PM