    frost on compressor pipes



    Hi
    I have a problem with my refrigerator.
    The symptoms are as follows:
    -The freezing compartment doesn't freeze (temp is above 0 centigrade)
    - There is frost on one of the compressor pipes.

    some details on the fridge:
    it's a non-freeze fridge. There are 2 t-stats in the main section. There is a small air tunnel between the freezing compartment and the main section that is open and shut by one of the t-stats.

    I have already filled the system with ***** (waist of money), but it didn't help.

    I'd appretiate any help.
    If any other details are needed please tell me.
    BTW the fridge is an Israeli model (I live in Israel) Amcor XL500, if this helps.

    Thank you
    Gaby



  2. #2
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: frost on compressor pipes

    I think you have a coil frosted over, ie: not defrosting.
    Switch fridge off overnight completely, switch on again, see if fridge works ok for a while

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: frost on compressor pipes

    What maked you decide to fill it with refrigerant?

    Is the valve shutting properly between cold and freezing part?

    On one of the compressor pipes. Are there 2 compressors?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    May 2006
    Location
    USA
    Age
    67
    Posts
    8
    Rep Power
    0

    Re: frost on compressor pipes

    Sounds like you may have problems with your defrost timer or defrost heater. Turn timer until it drops into defrost and wait about 10 minutes and listen for the click of the defrost timer droping out of defrost. If it doesn't than replace timer. While it is in defrost you can take amp reading of refrig. to check if defrost heater is working. While in defrost mode the compressor and evap fan will drop of line.

  5. #5
    Join Date
    May 2006
    Location
    singapore
    Age
    51
    Posts
    8
    Rep Power
    0

    Re: frost on compressor pipes

    Hi,

    Like what most guys have replied, it could be a defrost timer or heater problem. But on top of that, it can also be a fan problem. The moment you shut the fridge door, the fan starts running and circulating the cold air. If fan is spoilt, the compartment can ice up. Most fridge do not have charging valves bcos, there's really no need to top up the gas unless there's a leak. Well, if it's a leak, then topping it up is just waiting for another leak to occur isn't it?

Similar Threads

  1. Leaking frost free fridge-freezer
    By diment01 in forum Domestic
    Replies: 5
    Last Post: 22-06-2006, 11:49 PM
  2. Frost Project
    By JimmyMurphy in forum Domestic
    Replies: 1
    Last Post: 10-06-2006, 06:00 AM
  3. distributor frost
    By Lc_shi in forum Fundamentals
    Replies: 1
    Last Post: 04-03-2006, 08:12 AM
  4. frost free's the death knell!!
    By billyfridge in forum Domestic
    Replies: 5
    Last Post: 20-06-2005, 10:58 AM
  5. frost top construction ???
    By Tom Richardson in forum Fundamentals
    Replies: 174
    Last Post: 18-08-2003, 04:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •