Results 1 to 8 of 8
  1. #1
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Sab163 HF unloading problem



    Dear all,
    Hi,

    Sab163hf not unloading. I checked slide valve, NO,NC solenoid valves, position transmitter every thing fine. When comp. goes to 100% and then try to unload but not unloading. On 80% or less compressor unloading.
    Please suggest me what to do more.



  2. #2
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Re: Sab163 HF unloading problem

    When compressor continues run the low pressure warning on unisab II . For cross check I closed throttle valve on unloading EVM. Capacity remain on 100% then stop compressor I throttle to open then capacity being uploaded.
    Even on 100% compressor stop then compressor unloaded from 100%.

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Sab163 HF unloading problem

    Hi
    There is three things
    One your current if goes high than you set
    Another is you low pressure stop you go for more load
    3)your volume capacity in slide valve

  4. #4
    Join Date
    Oct 2016
    Location
    Serbia
    Age
    51
    Posts
    110
    Rep Power
    8

    Re: Sab163 HF unloading problem

    Hi Shaaf,
    this is very often on this type of compressor.
    When you reach 100% slide stop(volume) and capacity slide meet and stick like with glue.
    Sometimes problem is dirty oil or mineral oil used.
    Solution is to make modifications in compresor.

    best regards
    AKI

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Sab163 HF unloading problem

    Shaft,
    How many hours on compressor since last device?
    Had similar problem, ended up being one of the solenoids not operating correctly.
    When compressor turned off in loaded position, unloading occurs not through solenoids, but a small non return valve in unload pushrod, in discharge port (202 machines)assume the same for 163.
    Mother possibilities could be slide valve or guide wear.

  6. #6
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Re: Sab163 HF unloading problem

    Compressor in stop position unload via same way through unloading solenoid valve. Because I stopped throttle valve before stop compressor and compressor remain same position where it was stuck during running. After ten minutes I throttle to open and compressor starting to unload.

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Sab163 HF unloading problem

    Shaaf, are needle valves on solenoid block fully open?

    If you manually bled oil from cylinder while it was loaded by loosening fitting , see if unloads.

    What system do you have for slide valve indication?
    Is it rotating dial or linear position indicator, is it ready correctly?
    Last edited by RANGER1; 21-03-2017 at 09:35 PM.

  8. #8
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Re: Sab163 HF unloading problem

    Yes needle valve on unload side fully open.
    For slide valve indication linear position indicator.