15-03-2017, 01:36 PM #1
Evaporator or Condenser Tubes Bundles Allowable percentage plugging
Dear Friends,
Hi, We have YORK Johnson Controls Centrifugal Water Chillers that diagnosed has evaporator tubes were leaking due to tube freezing. Is there any articles for allowable percentage of tube to be plug for repair. Or even any OEM stated these tolerances?
Thanks in advance in your comments.
-
15-03-2017, 09:38 PM #2
Re: Evaporator or Condenser Tubes Bundles Allowable percentage plugging
Have you had an eddy test carried out on the tubes?
You don't want to plug any more than 10% of the number of tubes.The difference between genius and stupidity is that genius has its limits.
Marc
-
16-03-2017, 01:10 PM #3
Re: Evaporator or Condenser Tubes Bundles Allowable percentage plugging
Hi marc5180,
Yes, we carried out eddy current test, the results were:
Evaporator has 13.3 % tubes leaking, plus 8% thinning of tubes, for a total of 21.3% tubes were defective. That means, not a good idea to plug the tubes. Instead, is it re-tubing of evaporator tubes bundle?
Thanks for your comment.
-
16-03-2017, 07:58 PM #4
Re: Evaporator or Condenser Tubes Bundles Allowable percentage plugging
Hi Xelazman,
With 21% of the tubes defective then yes, your only option is to replace/retube.The difference between genius and stupidity is that genius has its limits.
Marc