    Low pressure switch (another newbie question!)



    Hi everyone

    Another newbie question I'm afraid, hopefully someone can help me understand!

    The low pressure switch... obviously it's on the low suction side of the compressor, I remember that from my course a few months ago. But, is the switch activated when the pressure is too low or too high?

    The engineer in me says if it's saying 'pressure too low in LP side' it must be that there is a blockage in the circuit somewhere. Maybe the expansion valve is stuck (can that happen?) or perhaps the solenoid valve is not activating (it has voltage on it).

    However if it is saying the pressure is too high on the LP side I'm lost... actually now I have written this I'm starting to think it must mean the opposite.

    Can anyone give me a pointer, please?

    Chris



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Low pressure switch (another newbie question!)

    The low pressure switch will normally open the circuit in the event of a pressure lower than the set point as it acts as a safety in the event of low pressure.
    You are quite right in that it could be a blockage, the solenoid not lifting or good old fashioned lost its gas charge.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Feb 2017
    Location
    UK
    Age
    44
    Posts
    8
    Rep Power
    0

    Re: Low pressure switch (another newbie question!)

    Thanks. That's what I thought, but wanted to check.

    I'll check the solenoid next time I am there.

    Chris

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Low pressure switch (another newbie question!)

    LPS is widely used to activate capacity control elements such as HGB and compressor's steps to keep certain procedures from freezing.

    When pressure drops below 0C, it closes the contacts.

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Low pressure switch (another newbie question!)

    Hi
    LPS can use for alt of fonction
    Limit for pressure come down from set point
    Used for unloading system sometimes
    Used for starting system sometimes
    Used for starting fan or solinoid valve in blast frizer
    So it depend on how we use it in our system and we disign it