Results 1 to 5 of 5

Thread: Vent line

  1. #1
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Vent line



    Hi friends,

    Would you please let me know in this type of receiver "Surge type" where we should install vent line ?

    Sincerely yours.
    112.jpg



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Vent line

    I think where you have it, is OK.
    Assuming this line is connecting into main compressor discharge line, which I would call a "Balance" line.

  3. #3
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Vent line

    As Ranger says it should vent back to the condenser inlet pipe

  4. #4
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Re: Vent line

    Dear Friends,

    Thanks for your help. OK , Why in this type of receiver tanks we can have sub-cool liquid ?

    Sincerely yours.

  5. #5
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Vent line

    Saturation is the equilibrium state at the surface of the liquid in the receiver. So should liquid as returned from the condenser be colder than the saturation corresponding to the condensing pressure and the liquid flow to the low side downstream of the receiver be equal to or less than the rate at which the condensers are delivering, the liquid flow will go right past the receiver and remain colder than the apparent saturation temperature.....