    Re: control stepless screw compressors

    Hi,

    Late arrival here..

    Good advice All!

    How's about a calculation of Actual Running Amps versus Full Load Amps (inferring Load)

    Yes, it only applies when running & we will not see 0% neatly through 100% but I'd still expect the value to be repeatable and meaningful..

    Happy tinkering

  2. #2
    Join Date
    Jul 2014
    Location
    israel
    Posts
    5
    Rep Power
    0

    Re: control stepless screw compressors

    the problem is the current is change
    from my experience the minimum and maximum is change in cold or hot day
    So if you want to knew that the first compressor is full load before startup the second compressor it's a problem

  3. #3
    Join Date
    Jul 2014
    Location
    israel
    Posts
    5
    Rep Power
    0

    Re: control stepless screw compressors

    From my experience the minimum and maximum is change in cold or hot day
    So if you want to knew that the first compressor is full load before startup the second compressor it's a problem

  4. #4
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: control stepless screw compressors

    Quote Originally Posted by ARIEL979 View Post
    From my experience the minimum and maximum is change in cold or hot day
    So if you want to knew that the first compressor is full load before startup the second compressor it's a problem
    Use time delay.
    Assume that it takes compressor 1 min. to increase capacity from 0% to 100%. If suction pressure above set point for 2 min. second compressor can start and you know that first compressor is fully loaded.