Thread: Expansion valve
    Mar 2016
    IRAN
    158
    3
    Expansion valve
    Dear Friends,
    Would you please let me know why on all catalogues show that we must install equalizer line after bulb of expansion valves ?
    Find my photo below.
    Sincerely yours.
    Aug 2009
    New Zealand
    54
    2,556
    Re: Expansion valve
    In the past when manufacturing was not as good as today, the seal between the equalized chamber and the main refrigerant flow was not always perfect. A small amount of refrigerant could pass down the equalizing line, Generally not enough to effect the refrigeration process, but enough to effect the sensing temperature at the bulb, if it were fitted before the bulb. So that is why it is fitted after the bulb.
    Mar 2016
    IRAN
    158
    3
    Re: Expansion valve
    Quote Originally Posted by mad fridgie View Post
    Thanks for your help
    Sep 2008
    Canada
    776
    12
    Re: Expansion valve
    TEVs with equalizing lines use for the evaporators with significant pressure drop. Equalizing line gives pressure in the bulb area to TEV to provide correct feeding. Evaporators with small pressure drop don't have equalizing line. In your drawing distributor gives significant pressure drop.