Hi Guys.
Just for interest.
I recently had to strip down a Danfoss ICM Valve, which was suspected of not shutting down the liquid refrigerant line it was in.
The first 2 pictures are the new valve and new seat in the old housing.
Pic 3 is what's left of the old seat next to the picture of what it should look like. (Item 2)
$ and 5 are as found when the ICM was opened!
Once rebuilt the refrigerant control was regained.
Grizzly






good valve seat ICM 20.jpgnew seal in valve body.jpgold damaged valve seat with diag item 2.jpgworn Valve Body.jpgworn valve seat.jpg