Thread: Inverter board

  1. #1
    Join Date
    Feb 2017
    Location
    Ireland
    Posts
    9
    Rep Power
    0

    Inverter board



    Hi there I was wondering mcb keeps tripping, windings are ok not mechanical seized I was wondering would my inverter board trip the breaker if faulty the second I turn isolator at outdoor mcb trips at mains



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Inverter board

    On what system? I assume an AC system and not a VSD?

    If you mean on an AC system then yes it could do, especially if the noise filter board has also failed.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Feb 2017
    Location
    Ireland
    Posts
    9
    Rep Power
    0

    Re: Inverter board

    Yes on a/c system it's a 3 phase compressor first I thought short circuit or grounded but resistance on windings are good I had 2.5 ohms across each winding and carried out megger test so then I thought mechanical but it's tripping even before compressor is called for.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Inverter board

    what type of breaker ? b type typically for lights and sockets c an d type for ac units /motors- will take more of an inrush

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Inverter board

    You have checked the 3 phase rotary isolator haven't you? There could be a dead short in there, maybe water has got in.
    It's worth confirming that first.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Join Date
    Feb 2017
    Location
    Ireland
    Posts
    9
    Rep Power
    0

    Re: Inverter board

    It's an c rated breaker..I need to call back and go through everything as I don't believe my compressor is causing the fault.is it possible winding insulation it badly damaged making compressor pull more current without giving me a short circuit or ground reading that there about to go.

  7. #7
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Inverter board

    If the winding insulation was bad, you would have picked it up on the insulation and resistance test.

    Why not disconnect the compressor terminals to rule the compressor out for certain.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  8. #8
    Join Date
    Feb 2017
    Location
    Ireland
    Posts
    9
    Rep Power
    0

    Re: Inverter board

    Il have to do that in the morning first thing and go form there.thanks for the help

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Inverter board

    inverter would detect overcurrent before a breaker trips

  10. #10
    Join Date
    Feb 2017
    Location
    Ireland
    Posts
    9
    Rep Power
    0

    Re: Inverter board

    Ended up being inverter board and noise filter blown.i disconnected compressor still tripping