Results 1 to 10 of 10
Thread: Inverter board
    Feb 2017
    Ireland
    9
    Inverter board
    Hi there I was wondering mcb keeps tripping, windings are ok not mechanical seized I was wondering would my inverter board trip the breaker if faulty the second I turn isolator at outdoor mcb trips at mains
    Mar 2006
    Lancashire
    1,859
    28
    Re: Inverter board
    On what system? I assume an AC system and not a VSD?
    If you mean on an AC system then yes it could do, especially if the noise filter board has also failed.
    Marc
    Feb 2017
    Ireland
    9
    Re: Inverter board
    Yes on a/c system it's a 3 phase compressor first I thought short circuit or grounded but resistance on windings are good I had 2.5 ohms across each winding and carried out megger test so then I thought mechanical but it's tripping even before compressor is called for.
    manchester
    5,639
    Re: Inverter board
    what type of breaker ? b type typically for lights and sockets c an d type for ac units /motors- will take more of an inrush
    Mar 2006
    Lancashire
    1,859
    28
    Re: Inverter board
    You have checked the 3 phase rotary isolator haven't you? There could be a dead short in there, maybe water has got in.
    It's worth confirming that first.
    Marc
    Feb 2017
    Ireland
    9
    Re: Inverter board
    It's an c rated breaker..I need to call back and go through everything as I don't believe my compressor is causing the fault.is it possible winding insulation it badly damaged making compressor pull more current without giving me a short circuit or ground reading that there about to go.
    Mar 2006
    Lancashire
    1,859
    28
    Re: Inverter board
    If the winding insulation was bad, you would have picked it up on the insulation and resistance test.
    Why not disconnect the compressor terminals to rule the compressor out for certain.
    Marc
    Feb 2017
    Ireland
    9
    Re: Inverter board
    Il have to do that in the morning first thing and go form there.thanks for the help
    manchester
    5,639
    Re: Inverter board
    inverter would detect overcurrent before a breaker trips
    Feb 2017
    Ireland
    9
    Re: Inverter board
    Ended up being inverter board and noise filter blown.i disconnected compressor still tripping