    Dec 2010
    BR
    63
    7
    McQuay Chiller Pathfinder
    Hello mates, how are all you?
    Sirs, I'm having an issue by "Low Discharge Superheat" on a AWS INV 360.2 XE ST. My doubt is: How the Microtech III reconyze the "Discharge Temperature" to calculate the DSH? I couldn't find the Discharge Temperature Sensor on it. Someone can help?
    May 2009
    United Kingdom
    Re: McQuay Chiller Pathfinder
    Discharge superheat = saturated discharge temp - discharge temp
    Apr 2011
    Russia
    139
    If it is Microtech-III the discharge sensor is DT-1 on wiring diagram. Check input X1 on board C.C.1