    McQuay Chiller Pathfinder



    Hello mates, how are all you?
    Sirs, I'm having an issue by "Low Discharge Superheat" on a AWS INV 360.2 XE ST. My doubt is: How the Microtech III reconyze the "Discharge Temperature" to calculate the DSH? I couldn't find the Discharge Temperature Sensor on it. Someone can help?



  2. #2
    Join Date
    May 2009
    Location
    United Kingdom
    Posts
    6
    Rep Power
    0

    Re: McQuay Chiller Pathfinder

    Discharge superheat = saturated discharge temp - discharge temp

  3. #3
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    15

    Re: McQuay Chiller Pathfinder

    If it is Microtech-III the discharge sensor is DT-1 on wiring diagram. Check input X1 on board C.C.1